    got one thats making thick ice...is that a function of the water level device?
    Let's give nukes a chance.

  2. #2
    Join Date
    Dec 2010
    Location
    Woodbridge Twp, NJ
    Posts
    1,307
    nope-its the function of a bad water inlet valve. Water is leaking in causing a long freeze and subsequent freeze-up. After tank is full and unit is in freeze, pull the tube out of the tank and unplug the power from the valve. If any water comes out, you got a bad valve.
    Every customer you take for granted today will be someone else's tomorrow.

  3. #3
    Join Date
    May 2005
    Posts
    1,349
    at the front of the cycle, it will power open once or twice, i can see through the clear tube that
    water isn't going in after those two additional water "hits"..


    i installed this machine in2000, and the water inlet valve was replaced in 06...

    but i will try your suggestion out tomorrow....

    as i said the machine will add a couple shots of water at the front end of the freeze cycle..
    Let's give nukes a chance.

  4. #4
    Join Date
    Dec 2010
    Location
    Woodbridge Twp, NJ
    Posts
    1,307
    it usually does. It will fill and then hit it again about 2 min into freeze. It could be a little trickle but it will cause a big problem.

    If you're not getting extra water, then the unit isn't harvesting completely and making a batch on top of a batch. Is the nickel flaked off the evap?
    Every customer you take for granted today will be someone else's tomorrow.

  5. #5
    Join Date
    May 2005
    Posts
    1,349
    the evaporators look better than new..
    ill go back up there and watch the harvest and water fill.
    Let's give nukes a chance.

  6. #6
    Join Date
    Jan 2007
    Location
    Southeast, GA / Jacksonville, FL
    Posts
    263
    I also thought that the float controlled ice thickness.

  7. #7
    Join Date
    Mar 2013
    Posts
    7
    Quote Originally Posted by navyhydronics View Post
    I also thought that the float controlled ice thickness.
    It does control thickness. What Dan is getting at is that if the water solenoid is trickling through it will make the water level sensor think that it is not freezing the water to make ice. With the solenoid sticking open (full flow) it will kick the machine off because of a long freeze cycle but with it trickling through it will just make the ice thicker.. I've actually come across both situations in the last week. We have terrible water up here and nobody thinks that they need filters installed anymore.


    Sent from my iStone using Tapatalk

  8. #8
    Join Date
    May 2005
    Posts
    1,349
    well he's what i found.....so far.....ice not falling off of rear evaporator...put the gauges on and found system running very low head psi..like 60...i shut the water inlet valve off and head went to 150...so i ordered a new water valve..

    system makes great ice, just won't dump it...
    Let's give nukes a chance.

  9. #9
    Join Date
    Jul 2005
    Location
    Phoenix, AZ
    Posts
    266
    Does anybody still have plating on the evaporators of these CME machines. It seems like every one I go up to had the plating coming off or completely gone.

    Sent from my DROID RAZR using Tapatalk 2

  10. #10
    Join Date
    May 2005
    Posts
    1,349
    this unit has all the plating on it, the system is at a mountain resort and is used 6 months out of 12, its 13 years old now...looks brand new.
    Let's give nukes a chance.

  11. #11
    Join Date
    Feb 2006
    Location
    Phoenix,AZ
    Posts
    2,876
    Quote Originally Posted by primmers View Post
    well he's what i found.....so far.....ice not falling off of rear evaporator...put the gauges on and found system running very low head psi..like 60...i shut the water inlet valve off and head went to 150...so i ordered a new water valve..

    system makes great ice, just won't dump it...
    60 psi in freeze. Or do you mean your suction was 60 in harvest? This is a water cooled machine correct? Shut off the machine and see i if you have condensor water still flowing. You shouldn't have any!

  12. #12
    Join Date
    May 2005
    Posts
    1,349
    60 psi head psi in freeze. yes theres water flowing when the system is off.
    Let's give nukes a chance.

  13. #13
    Join Date
    Feb 2006
    Location
    Phoenix,AZ
    Posts
    2,876
    Quote Originally Posted by primmers View Post
    60 psi head psi in freeze. yes theres water flowing when the system is off.
    I would start at the water (head) regulating valve. Sounds like it's stuck open!

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event