Flow Change Rate to a Carrier 30HXA chiller
Does anyone know where I can find the flow change rate to a Carrier model: 30HXA186RZ-630ZB. The cooler mod is: 10HX400013. The reason I ask is that I'm looking at going to variable flow using a primary pump. I have two of these chillers piped in parallel and would like to know if the chillers could handle this.
More information is posted in the controls forum under pressure tranducers and VFDs. Any help would be appreciated.Last edited by whec720; 02-12-2007 at 01:09 PM. Reason: mis-spell
"Excellence is the gradual result of always striving to do better"
-Pat Riley
-
02-12-2007, 11:12 PM #2
Professional Member
- Join Date
- Jan 2005
- Posts
- 587
Well ya might check out Carrier's literature available on their site.
Start here http://www.xpedio.carrier.com/idc/gr...t/30hx-6pd.pdf
Check out page 20, Application Data, gives min. flow rates. You will certainly be changing the selection data for the existing chillers. Some of what you may want to do may be trial and error. Not sure.
-
02-12-2007, 11:16 PM #3
Professional Member
- Join Date
- Jan 2005
- Posts
- 587
Here's a quote from the Application Data
"Variable cooler flow rates — These variable rates may
be applied to standard 30HX series chillers. However, the
unit will attempt to maintain a constant leaving chilled-fluid
temperature. In such cases, minimum fluid loop volume
must be in excess of 3 gpm per ton (3.2 L per kW) and
flow rate must change in steps of less than 10% per
minute. Apply 6 gal per ton (6.5 L per kW) fluid loop volume
minimum if flow rate changes more rapidly."
-