    I don't see those numbers either SR.
    You must be reading a S model somewhere and not the Q# you posted
    They don't publish the SC numbers but 4 imo is low also.
    You can't go wrong by cleaning it too............ unless you use the wrong cleaner
    “If You Can Dodge A Wrench You Can Dodge A Ball”

  2. #15
    Join Date
    Apr 2013
    Location
    In my head
    Posts
    321
    Quote Originally Posted by itsiceman View Post
    I don't see those numbers either SR.
    You must be reading a S model somewhere and not the Q# you posted
    You're exactly right, I was reading another model's operating pressure. Your original post was correct, I should be at 18-22...which gives me an evap of about -20.

    I'll try cleaning and report back....

  3. #16
    Join Date
    Apr 2013
    Location
    In my head
    Posts
    321
    Just wanted to also say Itsiceman I really appreciate your help, I'm learning a ton, love this forum!

  4. #17
    Join Date
    Mar 2007
    Location
    wedged in freezer shelf
    Posts
    7,210
    Quote Originally Posted by Servicerunner View Post
    I'll try cleaning and report back....
    Bring leak detector some gas and a scale too
    “If You Can Dodge A Wrench You Can Dodge A Ball”

  5. #18
    Join Date
    Feb 2010
    Location
    Newnan Ga,
    Posts
    183

    just my 2 pennies...

    If it were my call I would get the machine as close back to square one as possible, super clean condenser,descale,recover.refrigerant weigh in-out then acess possibilities.I have had the situation where all is perfect until night time the customer has a new mgr. They turn the A/C off or back at close and the machine bakes in its own heat.causing to throw a code and shutting down by the time service tech gets there the A/C is back on and all seems normal. Also add in the diagnosis of hot or warm water entering the machine. That coupled with dirty condenser and or overcharge would trip a high temp alarm. Just keep in mind the fan cycle is there to help aid the higher head pressure needed for adequate "heat" for harvest in a cuber not in a shaver.

Page 2 of 2 FirstFirst 12

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event