Page 3 of 4 FirstFirst 1234 LastLast
Results 27 to 39 of 50
  1. #27
    Sep 2012
    We had a tech come out the other day and he lowered the blower speed for the system. It now runs around 675 cfm for the first 7 minutes then ramps up to 824 cfm after that. Is this proper?
  2. #28
    Arizona
    Yup. That will work
    Make your expertise uniquely valuable.
    Make your influence uniquely far-reaching.
  3. #29
    Saint Joseph, MI
    Quote Originally Posted by 545GAlady View Post
    That will help. Even better is a thermostat that measures humidity and tells the unit to slow the blower in demand. IMO, this should be standard on ALL installation in all but hot dry climates.
  4. #30
    Sep 2012
    Thanks for the info guys. I just felt the air temperature and it's still not very cold. I went outside to look at the A/C and I find several holes in the condenser coil. There's also a very high pitched noise coming from the A/C as well. What could be wrong? Should I start another thread for this next issue? I'll have to call a service tech back out.
  5. #31
    south louisiana
    keep it all in one thread makes it easier to see where we
    have been rather than searching out different threads.
    best of luck.
  6. #32
    Sep 2012
    Ok thanks! We believe it was vandalism that caused the holes. All of the refrigerant leaked out and now the unit won't turn on (except the blower). Our HVAC company is coming out on Tuesday next week to look at the system and might quote us on a condenser coil replacement or a whole new A/C unit. It's a shame to have this happen on a 1 year old unit.
  7. #33
    Sep 2012
    Since the unit won't turn on at all now, do you think the compressor burned out because of running when there's no refrigerant or is there a low pressure cut off switch that's preventing the unit to run? A tech is coming out in a few days and I have the system completely off now.
  8. #34
    Oct 2010
    Hopefully it has a low pressure switch that shuts down the unit in a lp situation. Is it bullet holes? I'd like to see a pic.
  9. #35
    Sep 2012
    Quote Originally Posted by jtrammel View Post
    I'm hoping it does too. The whole outdoor unit isn't turning on at all. Only the blower in the furnace turns on. There is 0 refrigerant in the whole system. It looks more like someone stuck a screw driver in several locations on the coil. I'll upload a picture when I get a chance.
  10. #36
    DC Metro Area (MD)
    Can you post the model number of the condenser as well? I think you mentioned once it was a Goodman/Amana SSX14, and if so then it has high and low pressure switches. Bigger concern is that system has been opened up to the atmosphere (moisture) for a prolonged period. Proper repair procedure is critical as far as evacuation and replacing the filter drier.
  11. #37
    Sep 2012
Size:  32.7 KBName:  DSC00582.jpg
Size:  52.6 KBName:  DSC00583.jpg
Size:  63.3 KBName:  DSC00584.jpg
Size:  60.1 KBName:  DSC00585.jpg
Size:  62.7 KBName:  DSC00586.jpg
    The hole in the second picture is where we think the refrigerant leaked out. When I went outside yesterday I heard a loud hissing noise coming from the unit.
  12. #38
    south louisiana
    are you sure it wasn't shot up with a gun?
    sorry to see this has happened, hopefully it
    can be repaired/replaced at little cost to you..
    best of luck.
  13. #39
    Sep 2012
    Quote Originally Posted by energy_rater_La View Post
    best of luck.
    Well I'm not completely sure. Not all the holes are big. Some are extremely tiny. Our area of town see very little crimes.