    Manual J Calc question:

    When doing a load calc on a home, or room by room calc, where is the perimeter of the home or room measured, on the interior of the room, or the exterior?
    Take for example a room surrounded by 14" thick brick walls, the area measurements of the room are going to be completely different if you include the whole wall as being conditioned space.
    I'm not trained & experience in Manual J's at all, but it seems logical to measure the inside perimeter, because we are not trying to condition the 14" thick brick walls.
    Any help is appreciated.
    An answer without a question is meaningless.
    Information without understanding is useless.
    You can lead a horse to water............
    http://www.mohomeenergyaudits.com

  2. #2
    Join Date
    Aug 2007
    Location
    Northern VA 38 degrees N by 76 degrees W
    Posts
    5,060
    Quote Originally Posted by tipsrfine View Post
    When doing a load calc on a home, or room by room calc, where is the perimeter of the home or room measured, on the interior of the room, or the exterior?
    Take for example a room surrounded by 14" thick brick walls, the area measurements of the room are going to be completely different if you include the whole wall as being conditioned space.
    I'm not trained & experience in Manual J's at all, but it seems logical to measure the inside perimeter, because we are not trying to condition the 14" thick brick walls.
    Any help is appreciated.
    you are correct, it is the interior dimensions used for the calculation.

  3. #3
    Join Date
    Sep 2009
    Location
    Arnold mo
    Posts
    3,969
    Thanks. I have a contractor I'm working with who came in with a bid that appears to be oversized; he included the 16" thick walls in the rooms conditioned area.
    An answer without a question is meaningless.
    Information without understanding is useless.
    You can lead a horse to water............
    http://www.mohomeenergyaudits.com

  4. #4
    Join Date
    May 2012
    Location
    NC
    Posts
    50
    I am currently enrolled in a Residential design class, so my real world experience is very limited but I have the book with me.. We are using Manual Jae(Abridged Edition). It is not as many pages and much easier to teach from. It says in Appendix 5 that "Exposed above grade wall is recorded to the nearest foot(use the outside dimensions for exposed walls and the centerline dimension for interior partitions)". I have class on Tuesdays and I also have access to a Manual J. I'll ask my instructor and look at my Manual J and let you know what else I find.

  5. #5
    Join Date
    Dec 2002
    Location
    Arizona
    Posts
    4,416
    Your splitting hairs! Your wall load is a small fraction of you total load..........so if your off by a few sq' feet its NOTHING! Worry about your windows, there direction,there placement in the structure, there type, overhangs, and interior and exterior shading and blinds. And as you know Tips your inflitration is very important, don't forget about that blower door!
    Make your expertise uniquely valuable.

    Make your influence uniquely far-reaching.

  6. #6
    Join Date
    Dec 2002
    Location
    Arizona
    Posts
    4,416
    Quote Originally Posted by alamo1718 View Post
    I am currently enrolled in a Residential design class, so my real world experience is very limited but I have the book with me.. We are using Manual Jae(Abridged Edition). It is not as many pages and much easier to teach from. It says in Appendix 5 that "Exposed above grade wall is recorded to the nearest foot(use the outside dimensions for exposed walls and the centerline dimension for interior partitions)". I have class on Tuesdays and I also have access to a Manual J. I'll ask my instructor and look at my Manual J and let you know what else I find.
    You are correct! And yes the full Manual J8 reads the same as Manual J Abridged.
    Make your expertise uniquely valuable.

    Make your influence uniquely far-reaching.

  7. #7
    Join Date
    Aug 2001
    Location
    Mechanicsville, Virginia
    Posts
    1,398
    The OPs post is the kind of smart questions that need to be asked and answered. Splitting hairs? yes but a small miscalculation here and a mismeasurement there along with a few incorrect assumptions can send the end result far from acceptable accuracy. Be as precise as you can with measurements, and make as few as possible assumptions to get as close as you can to the actual load. Ideally: measure everything (twice) and assume nothing (if you can)

    Just don't follow the unofficial standard of measure sqft/ton and nothing else, or replace "Like with Like" and assume everything will be great.
    "If perfection is your goal, you may end up with good enough, what might you end up with when good enough is your goal?"
    efficientcomfort.net

  8. #8
    Join Date
    Feb 2010
    Location
    Cal
    Posts
    1,596
    Agreed, splitting hairs, but since he asked...

    Tips says hes not trying to condition the wall, but in reality you really are. Heat enters the wall structure and is transfered out at whatever rate. The surface area of both the interior and exterior matters, both conduct, and at different rates depending on which side is warmer. I cant comment on which dimension is the assumed dimension by the manJ folks.

    Me? Id measure the easiest way.

  9. #9
    Join Date
    Jun 2001
    Location
    Moore, Oklahoma, United States
    Posts
    4,378
    Fudging input data on indoor/outdoor temps will seriously throw things off.

  10. #10
    Join Date
    Dec 2002
    Location
    Arizona
    Posts
    4,416
    Tips here is some good info for you. AreYouUsingManualJ8Correctly.pdf
    Make your expertise uniquely valuable.

    Make your influence uniquely far-reaching.

  11. #11
    Join Date
    Aug 2011
    Location
    Natchitoches, Louisiana, United States
    Posts
    14
    Isn't that why we position the registers to sweep the perimeter walls?

  12. #12
    Join Date
    Sep 2009
    Location
    Arnold mo
    Posts
    3,969
    Wall thickness may not have a big difference normally, but consider a finished attic with knee walls. The actual conditioned space area can be much less than if you measured at the exterior walls. Take ceilings and how they are entered into Manual J. You don't ignore the ceiling and enter the roof dimensions. Same goes for knee walls. Common sense says that all we care about is the load on the conditioned space. If you built a small dog house in an attic and conditioned it, you wouldn't throw 2 tons of a/c into it just because the attic it is in is bigger.
    An answer without a question is meaningless.
    Information without understanding is useless.
    You can lead a horse to water............
    http://www.mohomeenergyaudits.com

  13. #13
    Join Date
    May 2007
    Location
    Dry as a bone Tucson
    Posts
    4,421
    Quote Originally Posted by second opinion View Post
    you are correct, it is the interior dimensions used for the calculation.
    According to appendix 5 it is the "outside dimensions" for exterior walls.
    Some Talk, Some Do
    "keeping condensing pressures low and evaporator pressures high"
    "Some customers are more interested in comfort than energy savings"
    Blog
    Web
    Facebook


Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event