    What is your best definition of a dry contact.
    It seems like there is as many different answers as there are dry contacts out there.

  2. #2
    Join Date
    May 2004
    Location
    Caldwell, ID
    Posts
    395
    Post Likes
    It means that the contact has no voltage attached to it. This contact can then be used as an input for a system separate than the one with the dry contact, and can be used with a separate power source.

    This is a generalization but I would say most dry contacts are rated for use up to 250V.

    For example, lets say the controller on my system, and all of main relay outputs operate on 24VAC. I have a seperate alarm contact that has an isolated common. You could then take my system, and hook up the alarm contact to a 120V light bulb, or to a 5VDC input on a PLC, etc.

  3. #3
    Join Date
    Jan 2007
    Location
    Milwaukee Wisconsin
    Posts
    1,002
    Post Likes
    Well said, Dry contacts require exteral power. "Wetted" contacts will read voltage supplied by the control.

  4. #4
    Join Date
    Aug 2006
    Posts
    23
    Post Likes
    Thanks for the reply, that was very easy to understand the way you put it.