Results 14 to 26 of 27
    Oct 2009
    Raleigh, NC
    Lots of walk-in coolers have off-cycle defrost timers.
    Apr 2013
    I have never seen a defrost timer in a walk in cooler, it should just be an off cycle defrost?
    Newnan Ga,
    Heatcraft puts defrost Grassilin clocks in all of their medium temp condensing units unless its a beer cooler we dont hook to them mostly because the worst thing one can do is loop a contactor coil through one of these. Does anyone know why its bad practice?
    May 2005
    no do tell cause i just did a install on a very large beer walk in and the timer is in the walkin..
    Let's give nukes a chance.
    Jul 2010
    So-Cal
    I'v added timers to coolers a few times! Nimrods wont keep the door closed.
    Jan 2010
    Quote Originally Posted by Grayline View Post
    Are you asking because you know or don't know ?
    Oct 2009
    Raleigh, NC
    It isn't bad practice. There are thousands and thousands of coolers running this way. Also, the timer usually cuts the LL solenoid, not the contactor.
    Sent from my ADR6350 using Tapatalk 2
    Jan 2010
    Quote Originally Posted by MicahWes View Post
    This would be true if the timer is located near the solenoid valve. Quite often I see the valve in the evaporator unit and the timer at the condensing unit with no interconnecting wiring.
    Southeastern Pa
    I want to know what the problem was that caused the OP to post this thread......!
    2 Tim 3:16-17
    Member, IAEI
    AOP Forum Rules:
    Oct 2008
    Quote Originally Posted by timebuilder View Post
    Was in a defrost cycle?
    "You never know what others don't know." -
    If I can't laugh at myself...then I'll laugh at YOU! -
    Apr 2013
    I know it has been a long time since I have posted but the call never came back in, until last night. Unit was short cycling, so again, grab the gauges and pump just a little 404 in to rise the pressure. Then I noticed the suction valve was bubbling like crazy, tightened down the packing nut and it stopped.
    I realize that 404 is a blend and there might be some issues down the road with refrigerant separation ( the proper term escapes me for the moment), but at least a leak was found, and yeah, no issues since that timer was reprogrammed, which I just eliminated it all together last night
    Oct 2009
    Raleigh, NC
    Are you talking about the suction service valve? It probably didn't leak when properly back-seated.
    If this was indeed the only leak, and it was on suction side, you won't have any fractionation problems with the remaining charge.
    Jul 2010
    So-Cal
    Yes alot of times they will leak around the stem when you open the valve. You need to check it when you close it (back seated) If you dident then you might have a leak else where.