    Tridium R2 Alarms/e-mails

    I have a job comming up alarming a cellular switch site with a stand alone jace to send out emails and i was wondering if anyone knows how to limit the emails sent out so it doesnt fill up the customers email boxes. TIA

  2. #2
    Basically, you cannot limit the numbers of emails, but you can adjust the sensitivity(deadband, delay, ect. ) of alarms.

  3. #3
    Join Date
    Mar 2005
    Location
    Virginia
    Posts
    1,144
    Guess that is one of the features added in AX?

  4. #4
    You mean "max sendable per day"? Yes.
    Quote Originally Posted by codewriter View Post
    Guess that is one of the features added in AX?

  5. #5
    Join Date
    Apr 2003
    Location
    South Carolina
    Posts
    82
    why would you limit the amount of alarms. isn't that is the purpose of the alarm's

  6. #6
    Join Date
    Mar 2005
    Location
    Virginia
    Posts
    1,144
    For network issues, so that they dont get hit with 500 emails when they already know there is a major issue after they got hit with the first 50.

  7. #7
    Say you setup a low temperature alarm at 45F. Do you want to get just one alarm when the temperatue is 44F at 4:00am or get 100 same alarms during 4:00am and 4:10am, just because the reading is hunting around 45F(45.1,44.9, 45.2, 44.9, 45.3, 44.7.........)?
    Quote Originally Posted by yellowfrog76 View Post
    why would you limit the amount of alarms. isn't that is the purpose of the alarm's