    Quote Originally Posted by mason View Post
    You should try being in the awkward position of calling your boss 3 times in one summer to tell him his SON misdiagnosed a compressor and have that same son hate you for it. I could go on and on with all the times this happened.
    You win...that's awkward.

  2. #28
    Join Date
    May 2011
    Location
    NC Foothills
    Posts
    70
    Many moons ago when I was still gourd green I found a compressor contactor with a bad coil. Found it within minutes on a Carrier package unit. Thought to self oh yeah I got this! This heating and air gig is cake! All that could be made out on the coil was a 2. No problem thought, got this on the truck. Replaced the contactor and turned the machine on. Very briefly after the contactor pulled in is when I learned the difference between 24 volt controls and 208 ! Luckily I had stepped back from the machine and when the contactor exploded none of the shrapnel hit me. Always Always Always make sure of your voltage and if your company has arc flash protection for you use it!

  3. #29
    Join Date
    Jul 2007
    Location
    The Hot South
    Posts
    1,315
    Quote Originally Posted by HVAC_Austin View Post
    Went to jump out a water source heat pump today using R to Y1 (the maintenance guys would of had to start it using their automated system, and they typically don't want to be bothered). It still wouldn't energize so I decided to take the jumper off (with 460 volts still flowing through). One side of my beautiful little magnetic jumper wire (those $10 yellow ones) popped off and instantly stuck to some other metal, apparently grounding the transformer. Sparks and smoke...kicked the breaker....so I ended up bothering the maintenance guys anyway (didn't know where the breaker box was).

    Hope this makes your day seem a little less worse.
    I'm still trying to figure out how you had 460 volts flowing through your jumper by jumping out R to Y1. Austin, can you elaborate on that?

  4. #30
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    18,360
    Quote Originally Posted by R123 View Post
    I'm still trying to figure out how you had 460 volts flowing through your jumper by jumping out R to Y1. Austin, can you elaborate on that?
    I "think" he means with 480 still flowing through the primary....
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist

    AOP Forum Rules:







  5. #31
    Join Date
    Jul 2007
    Location
    The Hot South
    Posts
    1,315
    Quote Originally Posted by timebuilder View Post
    I "think" he means with 480 still flowing through the primary....
    I've seen many 24 volt secondary's grounded (ie. weedeater or dog chewing up 24 volt t-stat wire at condensing unit), but have never in my life seen that trip a breaker or cause a significant spark that would cause smoke.....

  6. #32
    Join Date
    Nov 2011
    Location
    St. Louis
    Posts
    3,337
    Quote Originally Posted by R123 View Post
    I've seen many 24 volt secondary's grounded (ie. weedeater or dog chewing up 24 volt t-stat wire at condensing unit), but have never in my life seen that trip a breaker or cause a significant spark that would cause smoke.....
    But if a spring type gator clip being used on the secondary popped off and headed anywhere close to the contactor, you would flinch just as anyone of us would. I'm thinking that's what happened here. He was diagnosing with the unit energized and his little mag clips popped off and made contact with the primary load circuit at some point.

  7. #33
    Join Date
    Mar 2012
    Location
    Southern CA
    Posts
    30
    Those mag jumpers are an accident waiting to happen. You had a worst case scenario, but even if the thing had stuck to cabinet or the c terminal with low voltage on the other end you would have had a blown fuse or transformer (speaking from experience)
    Save those for recessed terminals like on a pcb connector and be very careful connecting them. If there is anything to grab, I'd stick to alligator clips, as much of a pain as they can be.
    -another tech slowly losing his green sheen

  8. #34
    Join Date
    Mar 2012
    Location
    Southern CA
    Posts
    30
    Blown control fuse, I mean

  9. #35
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    18,360
    One thing I noticed right away with the MagJumpers.

    Not all screws have enough ferrous material in their alloy to hold the jumper to the screw head tightly. Some screws have so little ferrous material in them that the mag jumper won't hold at all.

    IMHO, be ready to be underwhelmed if you buy a set.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist

    AOP Forum Rules:







  10. #36
    Join Date
    Dec 2012
    Location
    columbus, OH
    Posts
    2,032
    Thats all I need, a jumper attracted to conductive objects.

  11. #37
    Join Date
    Nov 2011
    Location
    St. Louis
    Posts
    3,337
    Quote Originally Posted by Core_d View Post
    Thats all I need, a jumper attracted to conductive objects.
    Good point.

    Yep...I thought they were the smartest thing when I saw them at Jmart. Now I only use them for Tstats...in other words, seldom.

Page 3 of 3 FirstFirst 123

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event