Trane RTAC EXV Replacement
Results 1 to 12 of 12
  1. #1
    Join Date
    Jan 2007
    Location
    Illinois
    Posts
    12

    Question Trane RTAC EXV Replacement

    I am going to be replacing an EXV in a few days. I need find out if any one has replaced one before?
    I have replaced a few boards before. I have Techview to bind the components.
    I've tried with Trane tech support and I was told the instructions come with the EXV.
    I also was told that I will need to remove all refrigerant to replace the EXV. Will I need to remove the refrigerant?
    Any help will be appreciated. Thanks in advance.

  2. #2
    Join Date
    Jul 2007
    Location
    The Hot South
    Posts
    1,288
    No need to remove all refrigerant, you can pump it down. No instructions come with EXV but you can follow standard refrigeration practices.

  3. #3
    Join Date
    Mar 2007
    Posts
    3,103
    Like R123 said, you can pump it down to make the repair. Do not power up the EXV before you install it. Use a back-up wrench and don't over-tighten the EXV in the valve body.
    "There is no greater inequality than the equal treatment of unequals."

    -Thomas Jefferson

  4. #4
    Join Date
    Mar 2004
    Location
    ottawa canada
    Posts
    1,990
    Quote Originally Posted by R123 View Post
    No need to remove all refrigerant, you can pump it down. No instructions come with EXV but you can follow standard refrigeration practices.
    Not if it doesnt have a suction valve and in the early days of the RTAC it was an option . Why anyone would order it without valves is beyond me but ??????
    The 64 roars to life Whoo hoo ...shes a rolling chassis .
    You bend em" I"ll mend em" !!!!!!!
    I"m not a service tech.. I"m a thermodynamic transfer analyst & strategic system sustainability specialist
    Best Austin Healey In Show twice in 2013 .....All those hrs paid off .

  5. #5
    Join Date
    Jul 2007
    Location
    The Hot South
    Posts
    1,288
    You can still pump it down without the suction valve. As a mater of fact, I've replaced many leaking suction valves. After it pumps down, close the discharge and oil valves.

  6. #6
    Join Date
    Jan 2007
    Location
    Illinois
    Posts
    12
    Thanks for all replies.
    I also found out today that the EXV is shorted. And the fuses on the board (EXV board, I am assuming) would blow.
    I was not the tech that condemned the parts. So, with that said, I don't think I can pump it down. Or can I? Thru TechView? I am going out there Friday to do some work on a couple VAVs. While I am there I will be able to see if there are valves on the chiller.

  7. #7
    Join Date
    Jul 2008
    Location
    NEW JERSEY
    Posts
    40
    Attach the replacement valve while still in the body and bind it. This will allow you to pump down the circuit. There is a service valve upstream of the EXV. Close it then pump down the circuit. Power down the chiller and replace the valve.

  8. #8
    Join Date
    Jul 2007
    Location
    The Hot South
    Posts
    1,288
    There is no EXV board, the EXV is a LLID and communicates directly with the DynaView. If the EXV is shorted and blowing the 3 amp fuse on the power supply, then you can disconnect the EXV and pump the circuit down without the EXV being operational. If the EXV is closed, then the refrigerant in the liquid line between the liquid line service valve and EXV will still be there so you will have to deal with that. There will be valves on the chiller and you can pump the circuit down through the DynaView (Service Pumpdown in the settings menu), or through TechView. Don't forget to close the oil scavenger line valve before you pump it down.

    Also, you only need to buy the EXV motor, not the whole valve. The motor just screws into the body.
    Also, don't ever power up the EXV without it in the body.

    I don't want to give any more info than this in the open chiller forum. You need to get your post count up to 15 and apply for pro membership.

  9. #9
    Join Date
    Jul 2007
    Location
    The Hot South
    Posts
    1,288
    Quote Originally Posted by Zeke XI View Post
    Attach the replacement valve while still in the body and bind it. This will allow you to pump down the circuit.
    There is no need to do this, the chiller will still pump down in pump down mode.

  10. #10
    Join Date
    Jan 2007
    Location
    Illinois
    Posts
    12
    To my understanding we just ordered the EXV motor.
    R123 , or any one. Can you possibly tell me where the oil scavenger line is to valve off? I need to read up as to apply for pro. Thanks

  11. #11
    Join Date
    Jul 2007
    Location
    The Hot South
    Posts
    1,288
    3/8 line on bottom of evap.

  12. #12
    Join Date
    Jan 2007
    Location
    Illinois
    Posts
    12
    Cool, I think I'm in good shape now.