    Cause of high pressure in heat pump heating.

    Hello All,
    Having an issue with a heat pump running at high discharge temp and pressure and tripping on high pressure. I pulled charge and weighed it back in. Was low on charge which was caused by a poor service port gasket. Unit runs a little longer and trips on high pressure. Filters good, coil clean, charge good. Suspect outdoor unit txv. Any input would be greatly appreciated.

  2. #2
    Join Date
    Dec 2005
    Location
    Cincinnati, Oh
    Posts
    4,923
    model numbers.
    "Better tell the sandman to stay away, because we're gonna be workin on this one all night."

    "Dude, you need more than 2 wires to a condenser to run a 2 stage heatpump."

    "Just get it done son."

    Dad adjusted

  3. #3
    Frigidaire FT4BF-060k

  4. #4
    Make sure the indoor coil is clean.

  5. #5
    Had a look and it is clean.

  6. #6
    Join Date
    Jul 2010
    Location
    clay county missouri
    Posts
    106
    Is there a filter drier? could the installer have allowed gunk/solder to block a line? During install over heated line overheating valve?
    Possible metering device clog/ malf.
    Maybe do temp check at discharge before port, after port, or maybe on line setup to metering device
    Top of head thought ymmv
    Sent from my LGL35G using Tapatalk 2

  7. #7
    Join Date
    Oct 2012
    Location
    Sacramento,ca
    Posts
    196
    Quote Originally Posted by Heatpump1$ View Post
    Hello All,
    Having an issue with a heat pump running at high discharge temp and pressure and tripping on high pressure. I pulled charge and weighed it back in. Was low on charge which was caused by a poor service port gasket. Unit runs a little longer and trips on high pressure. Filters good, coil clean, charge good. Suspect outdoor unit txv. Any input would be greatly appreciated.
    Whats you suction pressures at before it trips? Is there a charge chart on the panel of this unit that shows the pressures? Have seen many heat pumps that were weighed in be overcharged in heat mode.

  8. #8
    The unit was under charged upon first visit and it would trip sooner than with full charge. Suction pressure with correct charge stayed fairly constant but head pressure steadly climbed. Opening up tx only seemed to delay the high pressure trip. There was no pressure difference across the filter drier.

  9. #9
    to daniel87829,
    what is ymmv? Thanks

  10. #10
    I pulled 1.5# of charge out and this seems to have everything working good. First time I have overcharged by weighing at name plate. Every brand has their own quirks. Thank you everyone on your responses.

  11. #11
    Join Date
    Aug 2007
    Location
    Northern VA 38 degrees N by 76 degrees W
    Posts
    5,058
    Quote Originally Posted by Heatpump1$ View Post
    I pulled 1.5# of charge out and this seems to have everything working good. First time I have overcharged by weighing at name plate. Every brand has their own quirks. Thank you everyone on your responses.
    Nameplate charge means nothing unless you have the tested coil and line set, unless it is a package unit

  12. #12
    This installation is using an approved coil and I did not ad extra for the 35 foot lineset.

  13. #13
    Join Date
    Mar 2013
    Location
    Joplin,Missouri
    Posts
    310
    Is this a newer heat pump installed on an existing coil if so charging by weight on nameplate would probably be slightly overcharged. If you have checked temp across drier and indoor coil for cleanliness already than I would say outdoor TXV

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event