Results 1 to 13 of 18
    Apr 2013
    Cause of high pressure in heat pump heating.
    Hello All,
    Having an issue with a heat pump running at high discharge temp and pressure and tripping on high pressure. I pulled charge and weighed it back in. Was low on charge which was caused by a poor service port gasket. Unit runs a little longer and trips on high pressure. Filters good, coil clean, charge good. Suspect outdoor unit txv. Any input would be greatly appreciated.
    Cincinnati, Oh
    model numbers.
    "Just get it done son."
    Dad adjusted
    Apr 2013
    Frigidaire FT4BF-060k
    Apr 2013
    Make sure the indoor coil is clean.
    Apr 2013
    Had a look and it is clean.
    Jul 2010
    clay county missouri
    Is there a filter drier? could the installer have allowed gunk/solder to block a line? During install over heated line overheating valve?
    Possible metering device clog/ malf.
    Maybe do temp check at discharge before port, after port, or maybe on line setup to metering device
    Top of head thought ymmv
    Sent from my LGL35G using Tapatalk 2
    Oct 2012
    Sacramento,ca
    Quote Originally Posted by Heatpump1$ View Post
    Hello All,
    Whats you suction pressures at before it trips? Is there a charge chart on the panel of this unit that shows the pressures? Have seen many heat pumps that were weighed in be overcharged in heat mode.
    Apr 2013
    The unit was under charged upon first visit and it would trip sooner than with full charge. Suction pressure with correct charge stayed fairly constant but head pressure steadly climbed. Opening up tx only seemed to delay the high pressure trip. There was no pressure difference across the filter drier.
    Apr 2013
    to daniel87829,
    what is ymmv? Thanks
    Apr 2013
    I pulled 1.5# of charge out and this seems to have everything working good. First time I have overcharged by weighing at name plate. Every brand has their own quirks. Thank you everyone on your responses.
    Nameplate charge means nothing unless you have the tested coil and line set, unless it is a package unit
    Apr 2013
    This installation is using an approved coil and I did not ad extra for the 35 foot lineset.
    Mar 2013
    Joplin,Missouri
    Is this a newer heat pump installed on an existing coil if so charging by weight on nameplate would probably be slightly overcharged. If you have checked temp across drier and indoor coil for cleanliness already than I would say outdoor TXV