    receiver on a cap tube system

    On a reach in cooler is it wrong to have a condenser with a receiver? Thanks

  2. #2
    Join Date
    Nov 2010
    Location
    MN
    Posts
    134
    Not a good combo. What's the model # of this unit.

  3. #3
    Join Date
    Apr 2002
    Location
    Ann Arbor, MI
    Posts
    2,985
    Quote Originally Posted by oldpizzaguy View Post
    On a reach in cooler is it wrong to have a condenser with a receiver? Thanks
    A refrigeration system using a capillary tube expansion device is, by definition, a critically charged system.

    A refrigeration system using a receiver is, by definition, not a critically charged system.

    Attempting to apply a capillary tube on a system having a receiver is attempting a contradiction.
    If the only tool you have is a hammer, you tend to see every problem as a nail. – Abraham Maslow

  4. #4
    Join Date
    Jul 2012
    Location
    Western KY
    Posts
    1,221
    Normally no. Have seen some RIs with remote condensing units that has them, TXV set up though.

  5. #5
    Join Date
    Dec 2012
    Location
    columbus, OH
    Posts
    1,864
    According to nccer receivers are of little to no value with a fixed metering device. That gives me the impression that it wouldn't hurt anything but is pointless.

  6. #6
    Join Date
    Jul 2000
    Location
    Guayaquil EC
    Posts
    10,081
    A capillary tube cannot work properly with a receiver. Yes, you can get the system to cool, but that doesn't mean it's working right.

    Here's a past thread which gets into more detail on the subject: http://hvac-talk.com/vbb/showthread....-tube-question

  7. #7
    Join Date
    Feb 2005
    Location
    Tampa Florida
    Posts
    746
    Funny, I have several factory build systems that run from -60c to -150c with caps and receivers.

  8. #8
    Join Date
    Jul 2012
    Location
    Western KY
    Posts
    1,221
    Quote Originally Posted by jimp View Post
    Funny, I have several factory build systems that run from -60c to -150c with caps and receivers.
    ULT. Different animal.

  9. #9
    Join Date
    Jul 2000
    Location
    Guayaquil EC
    Posts
    10,081
    Quote Originally Posted by jimp View Post
    Funny, I have several factory build systems that run from -60c to -150c with caps and receivers.
    Do you have any piping diagrams for these? It would be interesting to see what they're doing differently.

  10. #10
    Join Date
    Aug 2002
    Location
    Southold.calm
    Posts
    4,856
    Quote Originally Posted by jimp View Post
    Funny, I have several factory build systems that run from -60c to -150c with caps and receivers.


    Our ULT are cap tube and no receivers

  11. #11
    Join Date
    Jul 2012
    Location
    Western KY
    Posts
    1,221
    Quote Originally Posted by pecmsg View Post
    Our ULT are cap tube and no receivers
    Maybe he's talking about an HX. Kinda looks like a receiver.

  12. #12
    Join Date
    Apr 2010
    Location
    San Diego, CA
    Posts
    172
    Expansion chamber...

  13. #13
    Join Date
    Jul 2000
    Location
    Guayaquil EC
    Posts
    10,081
    Quote Originally Posted by cmclifton View Post
    Expansion chamber...
    While that would be considered a receiver...technically, it's not exactly the type we were referring to.

    Perhaps jimp is just having a bit of fun.

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event