    100+pound recovery machine?

    Could anyone recommend a setup for recovering a large amount of refrigerant quickly? I currently use a Promax RG6000 which is good but very slow.

    Thanks for any ideas

  2. #2
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    4,378
    Quote Originally Posted by DeltaTech View Post
    Could anyone recommend a setup for recovering a large amount of refrigerant quickly? I currently use a Promax RG6000 which is good but very slow.

    Thanks for any ideas
    what is a large amount to you? 100# or 1000# or 10,000#?
    "Mother" is the name for God on the lips and hearts of children....The Crow

  3. #3
    Join Date
    Mar 2009
    Location
    Mid-Mo
    Posts
    3,595
    Quote Originally Posted by jayguy View Post
    what is a large amount to you? 100# or 1000# or 10,000#?
    ^^^

  4. #4
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    25,667
    Don't use the recovery machine for large amounts of refrigerant removal, providing that the machine itself still runs.

    Only use that to "clean up"

  5. #5
    Join Date
    Apr 2009
    Location
    Rio Vista CA.
    Posts
    37
    Sorry,
    I'm wondering if there is a recovery machine that would be able to remove 100lb quickly.

  6. #6
    Join Date
    Sep 2005
    Location
    Atlanta GA area
    Posts
    21,153
    The most efficient machine I know of for mid volume recovery tasks would be an Appion G5-twin.

    I would set it up in a 'push-pull' arrangement. Appions tend to pump liquid very efficiently, yet they are a bit slow cleaning the gas out on a hot day. I use a cooler after the recover pump;

    http://www.centurytool.net/MT69_CPS_..._p/cpsmt69.htm
    GA-HVAC-Tech

    Quality work at a fair price with excellent customer service!

    Romans Ch's 5-6-7-8

    2 Chronicles 7:14

  7. #7
    Join Date
    Mar 2009
    Location
    Mid-Mo
    Posts
    3,595
    We have an ice machine at the office that comes in handy. We took 2 55 falling antifreeze barrels and cut both the top and bottom off of one of them, then the top off the other. We put the 125 lb cylinder in the barrels and pack it with ice. Then run water over all of it and it works pretty fast.

    I bet these other guys have some better tricks....

  8. #8
    Join Date
    Apr 2009
    Location
    Rio Vista CA.
    Posts
    37
    Yes the unit I'm working on is running. I have 50lb recovery tanks. Could I attach a line from the unit liquid reciever to the liquid tank port and a line from a suction port to the tank vapor port and fill the tank with liquid from the reciever by gently bleeding the vapor to suction port? Would that be a quicker way?
    Quote Originally Posted by jpsmith1cm View Post
    Don't use the recovery machine for large amounts of refrigerant removal, providing that the machine itself still runs.

    Only use that to "clean up"

  9. #9
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    4,378
    Quote Originally Posted by DeltaTech View Post
    Yes the unit I'm working on is running. I have 50lb recovery tanks. Could I attach a line from the unit liquid reciever to the liquid tank port and a line from a suction port to the tank vapor port and fill the tank with liquid from the reciever by gently bleeding the vapor to suction port? Would that be a quicker way?
    you have to be careful doing that because you are also removing/storing the oil from the unit. the appion works pretty good and it is light weight. if you have access to the liquid receiver, then push-pull it and you will get it done pretty quickly. also, more tanks helps. if you have 100# to remove, it will take a long time using 2-50# tanks...take up 4-50# tanks and the recovery will go much faster.
    "Mother" is the name for God on the lips and hearts of children....The Crow

  10. #10
    Join Date
    Mar 2012
    Location
    Birmingham Al
    Posts
    252
    dry ice packing the recovery drum works very well for speeding the recovery process. also i have seen people use those "sub coolers" not sure if they are an available product or not but i have seen maybe 25 feet of copper coiled submerged in ice water attached to the discharge of the recovery machine. i would really think that a non leaking A coil submerged in ice water on the discharge would work great.