    MO99 vs 427A

    Just looking for some thoughts on the pro's and cons of each. With R22 heading toward $500 a can. It's just not an option anymore. But the amount of R22 equipment out there (allot of it still in very good condition) can't be ignored ether. Many customers are just not up to replacing their equipment yet.

  2. #2
    Join Date
    Oct 2010
    Location
    Anderson, South Carolina, United States
    Posts
    5,659
    Quote Originally Posted by EMC mech. View Post
    Just looking for some thoughts on the pro's and cons of each. With R22 heading toward $500 a can. It's just not an option anymore. But the amount of R22 equipment out there (allot of it still in very good condition) can't be ignored ether. Many customers are just not up to replacing their equipment yet.
    Find the leaks and fix them then top off with r22

  3. #3
    Join Date
    Apr 2013
    Location
    Phoenix, Arizona
    Posts
    6
    Quote Originally Posted by jtrammel View Post
    Find the leaks and fix them then top off with r22
    That doesn't work if the unit has a sever undercharge. But the question is which refrigerant have you found to work better for you MO99 or 427A

  4. #4
    Join Date
    Oct 2010
    Location
    Anderson, South Carolina, United States
    Posts
    5,659
    Quote Originally Posted by EMC mech. View Post
    That doesn't work if the unit has a sever undercharge. But the question is which refrigerant have you found to work better for you MO99 or 427A
    Have not used either and probably won't. I think 407c is what I would switch to if anything. It's a little more work but from the little research I've done it will match capacity/temps better than others. MO99 would be tempting since you don't have to change the oil out. If I do go this route I would first try it on some equipment at my shop to test it out. As for now, the customer has 4 choices: find/fix leak and charge with r22, charge with r22 and let er rip, change out with a new r410a system or find someone else to dump another refer in it.

  5. #5
    Join Date
    Apr 2013
    Location
    Phoenix, Arizona
    Posts
    6
    Quote Originally Posted by jtrammel View Post
    Have not used either and probably won't. I think 407c is what I would switch to if anything. It's a little more work but from the little research I've done it will match capacity/temps better than others. MO99 would be tempting since you don't have to change the oil out. If I do go this route I would first try it on some equipment at my shop to test it out. As for now, the customer has 4 choices: find/fix leak and charge with r22, charge with r22 and let er rip, change out with a new r410a system or find someone else to dump another refer in it.
    I have a couple of property's I work with that have equipment that is on the verge of replacement. Might be a good place to test.

  6. #6
    Join Date
    Oct 2010
    Location
    Anderson, South Carolina, United States
    Posts
    5,659
    Quote Originally Posted by EMC mech. View Post
    I have a couple of property's I work with that have equipment that is on the verge of replacement. Might be a good place to test.
    Just do your research and let the customer know what problems may arise (capacity/efficiency loss, longer run times, etc.)

  7. #7
    Join Date
    Apr 2013
    Location
    Phoenix, Arizona
    Posts
    6
    Quote Originally Posted by jtrammel View Post
    Just do your research and let the customer know what problems may arise (capacity/efficiency loss, longer run times, etc.)
    I've been looking at the data sheets for 427A and MO99. The compressor has to be cut and oil dumped and replaced for 427A. MO99 on the other hand is compatible with R22 oils and can be dropped in.

  8. #8
    Join Date
    Oct 2010
    Location
    Anderson, South Carolina, United States
    Posts
    5,659
    None of them can be dropped in on top of r22, charge must be removed and replaced. Some require a partial oil change while others do not.

  9. #9
    Join Date
    Jul 2012
    Location
    Richland, WA
    Posts
    234
    Have 4 RTU's (2 with 2 circuits (york) and 2 with 1 circuit (trane)) and a walkin freezer that have MO99 in them for about a year now and have not had any problems with them. All we had to do was change all the filter driers, and anything that has a o-ring on it in the system. R22 causes the seals to swell and MO99 with not.


    Sent from my iPhone using Tapatalk

  10. #10
    Join Date
    Apr 2013
    Location
    Phoenix, Arizona
    Posts
    6
    Quote Originally Posted by caheiman30 View Post
    Have 4 RTU's (2 with 2 circuits (york) and 2 with 1 circuit (trane)) and a walkin freezer that have MO99 in them for about a year now and have not had any problems with them. All we had to do was change all the filter driers, and anything that has a o-ring on it in the system. R22 causes the seals to swell and MO99 with not.


    Sent from my iPhone using Tapatalk
    Thanks I think I've come to a decision for my company. I've been reading the data on both. MO99 seems to be the way to go.

  11. #11
    Join Date
    Mar 2007
    Location
    Myrtle Beach, SC
    Posts
    2,919
    We tried M099 about 2 years ago on one system. So far, so good.
    Remember, Air Conditioning begins with AIR.

  12. #12
    Join Date
    Oct 2010
    Location
    Anderson, South Carolina, United States
    Posts
    5,659
    Doesn't MO99 cost within a couple dollars per lb of R22?

  13. #13
    Join Date
    Jul 2012
    Location
    Richland, WA
    Posts
    234
    R22 here in Washington is almost 500 per jug, MO99 is under 300 per jug. Just bought a jug of MO99 in January


    Sent from my iPhone using Tapatalk

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event