    ORI-ORD setup -- 350 lb head, 50 lb suction Problem

    Anyone have problems with this set-up before. I have clean filters liquid and suction. This is circuit B on a SA30 Desert-Aire heat recovery system serving a natatorium. Unit pressures are normal in cooling ( using outdoor condenser ) when in reheat (indoor condenser) I get a high headpressure and low suction pressure. But what is wierd is that sometimes the pressures are normal. Both condensers share the ORI-ORD the only thing that it also might be is the check valve sticking in partial open. My next move will be to take pressure and temperature drops across all the components. One thought I had was maybe the ORI bellows is leaking somehow and building internal pressure making the valve not open all the way. But this would affect the pressures of the outdoor condenser operation also? I have found that if I cycle the condensers (switch to outdoor and then back to indoor)the problem goes away for awhile. Thanks for any feedback.

  2. #2
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    5,661
    Post Likes
    Indoor coils are generally smaller than outdoor coils. With the set up you are using, you probably need a place for the extra refrigerant to go when you aren't using it like a receiver.

  3. #3
    Join Date
    Apr 2009
    Location
    Rio Vista CA.
    Posts
    51
    Post Likes
    The unit does have a reciever M/N UR108 I agree the reciever should be storing the extra refrigerant and not the condenser. It appears that the liquid is not being let out of the condenser when it should be. The 7/8 liquid line sight glass just before the expansion valve is also flashing (and when the pressures are normal it is not). I have a factory weighed in charge.

  4. #4
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,675
    Post Likes
    Remove the cap on the ORI valve. If it hisses and all returns to normal, replace it.

    They DO leak internally and it does affect their settings, typically in a manner similar to what you're describing.

  5. #5
    Join Date
    Jul 2000
    Location
    Guayaquil EC
    Posts
    12,560
    Post Likes
    Quote Originally Posted by jpsmith1cm View Post
    Remove the cap on the ORI valve. If it hisses and all returns to normal, replace it.

    They DO leak internally and it does affect their settings, typically in a manner similar to what you're describing.
    Some years ago, I had an ORI that did just that. It would take a couple of days to get a new valve, but I had to keep this rack running, so I brazed a 1/4" access valve onto the cap and vented it to suction.

    That little trick got me by until I got the new valve.

  6. #6
    Join Date
    Jan 2007
    Location
    Pittsburgh
    Posts
    182
    Post Likes
    Yes I have see a hand full of ORI failure, It had high head, very hot liquid line, sight glass flashing.. from what I experienced.

  7. #7
    Join Date
    Jun 2011
    Posts
    422
    Post Likes
    ORI-ORD? Open on Rise of...?

  8. #8
    Join Date
    Apr 2009
    Location
    Rio Vista CA.
    Posts
    51
    Post Likes
    ORI -- Opens on Rise of Inlet pressure ,, ORD -- Opens on Rise of Differential pressure