    YT refrigerant charge

    Trying to find factory charge by weight for two YT machines. One is r-11, about 25 yrs old. The other is 123, about 15 yrs old. Have found several manuals but nothing mentioning charge weights. Can anyone help?

  2. #2
    Join Date
    Feb 2013
    Location
    Phoenix, AZ
    Posts
    198
    Found this for YT style J Millenium for R123:

    YTstyleJ123.jpg

  3. #3
    Join Date
    Jan 2011
    Posts
    1,032
    Quote Originally Posted by murphman View Post
    Trying to find factory charge by weight for two YT machines. One is r-11, about 25 yrs old. The other is 123, about 15 yrs old. Have found several manuals but nothing mentioning charge weights. Can anyone help?
    Refrigerant charges weren't always the same from year to year. Need to know the complete model and the first four letters in the S/N to be sure. I think the chart posted above is too new to be accurate in your case. Style J chillers had completely different refrigerant charges than their earlier predecessors. If your chiller does NOT have an Optiview panel the numbers posted above are inaccurate.

  4. #4
    Join Date
    Feb 2013
    Location
    Phoenix, AZ
    Posts
    198
    Quote Originally Posted by KnewYork View Post
    Refrigerant charges weren't always the same from year to year. Need to know the complete model and the first four letters in the S/N to be sure. I think the chart posted above is too new to be accurate in your case. Style J chillers had completely different refrigerant charges than their earlier predecessors. If your chiller does NOT have an Optiview panel the numbers posted above are inaccurate.
    True, the manual was for YT's with Optiview.

  5. #5
    Join Date
    Apr 2009
    Posts
    15
    The 11 machine is YTK9L6F1-CVCS. Serial starts YESM. The 123 machine is YTL6D8F2-CWH. Serial starts GDEM. Any help appreciated.

  6. #6
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    4,005
    The YTK9L6F1-CVCS has 1350# of R11.

    The YTL6D8F2-CWH has 1590# of R123.
    It's tube brushing season...93% done (39.35 miles of tubing)...only 1,242 tubes to go!

    Original member of the Raccoon Brotherhood.

    EVERYTHING IS AWESOME!!!

  7. #7
    Join Date
    Apr 2009
    Posts
    15
    Thanks Jayguy

  8. #8
    Join Date
    Feb 2011
    Location
    OH
    Posts
    149
    Quote Originally Posted by murphman View Post
    Trying to find factory charge by weight for two YT machines. One is r-11, about 25 yrs old. The other is 123, about 15 yrs old. Have found several manuals but nothing mentioning charge weights. Can anyone help?
    depending what cooler you have j1 j3 1130 # alot of times if your machine is down 4hr or longer you can look in sight glass will be 1/2 +- 1/4 all pumps must be off. if you give model number i might have info on how much ref it takes . hope this helps.