Page 2 of 2 FirstFirst 12
Results 14 to 26 of 26

Thread: Heat Pumps?

  1. #14
    Join Date
    Jan 2004
    Location
    PA
    Posts
    74,070
    Post Likes
    Quote Originally Posted by MurDoc04 View Post
    I'm being to think my teach is a little out of touch on heat pumps and that irritates me because I'm paying for this school. Thank you fellows for the info.
    A few years back there was a thread or 2 about this in the Pro forums. I believe it was Normchris that posted that heat pumps are more efficient at 450 CFM per ton.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  2. #15
    Join Date
    Oct 2004
    Location
    Yakima, WA
    Posts
    1,841
    Post Likes
    Systems are designed for nominal 400 cfm per ton. The air handler doesn't differentiate between heat and cool modes, and a heat pump is an air conditioner first.

    Yes there are some exceptions - carrier built equipment is designed at 350, and one day every system will have a variable speed air handler and an inverter drive compressor, Skynet will become self-aware, and we will all be checking superheat in the matrix. Until then, 400 cfm per ton.

  3. #16
    Join Date
    Jan 2004
    Location
    PA
    Posts
    74,070
    Post Likes
    Quote Originally Posted by cjpwalker View Post
    Systems are designed for nominal 400 cfm per ton. The air handler doesn't differentiate between heat and cool modes, and a heat pump is an air conditioner first.

    Yes there are some exceptions - carrier built equipment is designed at 350, and one day every system will have a variable speed air handler and an inverter drive compressor, Skynet will become self-aware, and we will all be checking superheat in the matrix. Until then, 400 cfm per ton.
    Many systems are also commonly sized using .1" FR. Doesn't mean its right, its just commonly done.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  4. #17
    Join Date
    Jun 2011
    Location
    Orange, Tx
    Posts
    8
    Post Likes
    Thread Starter
    Just from this thread I understand more about heat pumps now. I'm still new to this field and I'm slowly learning but I'm getting there.

  5. #18
    Join Date
    Dec 2002
    Location
    Arizona
    Posts
    4,480
    Post Likes
    Quote Originally Posted by MurDoc04 View Post
    I know that it is standard 400 CFM per ton for residential AC / Heat... What is standard CFM for heat pumps? I have been told by my instructor that 450 is a rule if thumb but I can not find any hard evidence in that. Need some help please!
    I would order Manual S and H from ACCA's website and do a little reading. I just spent the week with the author of these two books ( along with Manual J and D) and believe me he's not into rule of thumbs!

    And 400cfm per ton on A/C is also BS.
    Make your expertise uniquely valuable.

    Make your influence uniquely far-reaching.

  6. #19
    Join Date
    Nov 2004
    Location
    SW FL
    Posts
    7,935
    Post Likes

    Thumbs up

    Quote Originally Posted by jimj View Post
    I would order Manual S and H from ACCA's website and do a little reading. I just spent the week with the author of these two books ( along with Manual J and D) and believe me he's not into rule of thumbs!

    And 400cfm per ton on A/C is also BS.
    RIGHT, 400 CFM/ ton +/-10% is a good observation
    _ and B asic S cience.

    Q = 1.08 * CFM * dT
    Q ton = 12,000
    SHR avg 0.75
    Q sensible 9,000 ______ 9,000 ____ 9,000
    dt = ____ 21 ______ 18 ________ 23
    _______ 1.08 ______ 1.08 ______ 1.08
    _ CFM 397 ____ 463 ____ 362
    Designer Dan
    It's Not Rocket Science, But It is SCIENCE with "Some Art". ___ ___ K EEP I T S IMPLE & S INCERE

    Define the Building Envelope and Perform a Detailed Load Calc: It's ALL About Windows and Make-up Air Requirements. Know Your Equipment Capabilities

  7. #20
    Join Date
    Dec 2002
    Location
    Arizona
    Posts
    4,480
    Post Likes
    Quote Originally Posted by dan sw fl View Post
    RIGHT, 400 CFM/ ton +/-10% is a good observation
    _ and B asic S cience.

    Q = 1.08 * CFM * dT
    Q ton = 12,000
    SHR avg 0.75
    Q sensible 9,000 ______ 9,000 ____ 9,000
    dt = ____ 21 ______ 18 ________ 23
    _______ 1.08 ______ 1.08 ______ 1.08
    _ CFM 397 ____ 463 ____ 362
    You would make Hank R proud!
    Make your expertise uniquely valuable.

    Make your influence uniquely far-reaching.

  8. #21
    Join Date
    Nov 2004
    Location
    SW FL
    Posts
    7,935
    Post Likes
    Quote Originally Posted by jimj View Post
    You would make Hank R proud!
    HVAC 101
    Q= 1.08 * CFM * dT
    Designer Dan
    It's Not Rocket Science, But It is SCIENCE with "Some Art". ___ ___ K EEP I T S IMPLE & S INCERE

    Define the Building Envelope and Perform a Detailed Load Calc: It's ALL About Windows and Make-up Air Requirements. Know Your Equipment Capabilities

  9. #22
    Join Date
    Oct 2004
    Location
    Yakima, WA
    Posts
    1,841
    Post Likes
    Ok, so 400cfm per ton is wrong... so walking up to a new system for a startup where do you set the blower? I always shoot for 400 per (nominal) ton based on TESP and fan charts.

  10. #23
    Join Date
    Nov 2004
    Location
    SW FL
    Posts
    7,935
    Post Likes
    Quote Originally Posted by cjpwalker View Post
    Ok, so 400cfm per ton is wrong... so walking up to a new system for a startup where do you set the blower? I always shoot for 400 per (nominal) ton based on TESP and fan charts.
    jumj from Arizona has a different xxxx xx thumb, perhaps, IT'S GREEN.!
    Designer Dan
    It's Not Rocket Science, But It is SCIENCE with "Some Art". ___ ___ K EEP I T S IMPLE & S INCERE

    Define the Building Envelope and Perform a Detailed Load Calc: It's ALL About Windows and Make-up Air Requirements. Know Your Equipment Capabilities

  11. #24
    Join Date
    Oct 2004
    Location
    Yakima, WA
    Posts
    1,841
    Post Likes
    So we actually learned it as Cooling BTUs = CFM x delta h x 4.5, h=enthalpy. CFM x 1.08 x dt is for heating. I've never learned to use it for cooling with 9000 btu sensible. Where does that number come from?

  12. #25
    Join Date
    Jan 2004
    Location
    PA
    Posts
    74,070
    Post Likes
    If your going for efficiency only, then 450 CFM for a heat pump. If for comfort in cooling then CFM should be set up to meet the SHR you need in cooling.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  13. #26
    Join Date
    Jan 2004
    Location
    PA
    Posts
    74,070
    Post Likes
    Quote Originally Posted by cjpwalker View Post
    So we actually learned it as Cooling BTUs = CFM x delta h x 4.5, h=enthalpy. CFM x 1.08 x dt is for heating. I've never learned to use it for cooling with 9000 btu sensible. Where does that number come from?
    1200X6.4*4.5=34,560 total BTUs.
    1200X20X1.08=25,920 sensible BTUs.
    34560-25920=8,640 latent BTUs.
    25920/34560=.75 SHR.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

Page 2 of 2 FirstFirst 12

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.