    Walk In freezer
    Do walk in freezers ever not use a defrost timer and/or a means of defrosting the coil. I recently did a startup on an exisiting walk in freezer and did not see time clock anywhere? I popped the side of the evaporator coil where the power was going in and didn't see any electric defrost heaters, fan delay/ defrost termination controls. Just 120v going to the fans.
    Oct 2011
    Chicagoland Area
    Could have hot gas defrost but it will still need a clock. They hide timeclocks in the strangest places sometimes
    Jul 2000
    Guayaquil, EC
    Check out the other end of the evaporator where the piping is. If it's hot gas defrost, there should be a tee after the TXV...among other possible goodies like a check valve, drain pan heater or a HG line if it's a three-pipe system.
    But as 2sac said, it'll still need a timeclock.
    Mar 2013
    thanks
    Oct 2009
    Raleigh, NC
    Modern freezers with EEV's and hot gas defrost won't have any tees or anything extra, besides maybe a pressure transducer and a thermister, in the unit cooler.
    Southeastern Pa
    I had a walk-in a few months ago where the time clock was built into the condensing unit on the roof.
    2 Tim 3:16-17
    Member, IAEI
    AOP Forum Rules:
    Oct 2009
    Raleigh, NC
    Most of the Heatcraft and similar condensing units now have a Grasslin in them. I rather like it there.
    Mar 2013
    Yea, on the condensing unit is where I usually find them. This unit definitly has it hidden somewhere strange .
    Oct 2009
    Raleigh, NC
    Does it have just a controller somewhere? If it does, then it handles defrost.
    Aug 2009
    Maine
    Years ago there was a laser like light that looked through the coil fins. When the light got blocked that was the signal for it to defrost. I think it was put in with an energy management system.
    I have a customer that has the clocks for the cooler and freezer behind a big mixer in a storage bin. If you sit on the mixer you can work on them ok.
    Quote Originally Posted by northeastbeast View Post
    OK, I'm confused...
    You did a "start-up" on an existing walk-in? How, exactly does one do this?
    Also, how do you complete a "start-up" without testing and verifying proper defrost operation and termination?
    When I read "start-up" I thought that it could simply have had the wrong evaporator installed. Stranger things have happened, although I would NOT want to be the guy responsible for that particular oopsie.
    Oct 2009
    Raleigh, NC
    I had to start up an existing walk-in last month. It had been shut down for two years. Maybe this is what he means?
    Aug 2009
    Maine
    To the best of my knowledge all commercial walk in freezers have to have a means to defrost. Period. BTW did you check both sides of the evap ?