    Mar 2013
    Both indoor and outdoor units are definitely 3 ton units, I checked them myself. The HVAC company changed the indoor unit from medium to high fan speed because one side of the house was cold. Maybe I should turn it back down to medium and play with the dampers instead.
    Dpes seem too far off to me. But I could have missed something. I'm not sure what city to use, but Richmond for example is 18F winter, 92 F summer. The whole state only ranges from 10F-25F(along coast) and 90-93F.
    He is in Winchester and winter ODAT is 10 and summer is 90 with 38 grains at 50%
    Fl
    My version of Wright J has two choices...
    Winchester Man J/N summer 90db/74wb winter 10
    or
    Winchester Rgnl ASHRAE 2009 summer 93db/74wb winter 18
    HVAC-Calc uses 90/10
    SW FL
    Was the Manual J used in permitting?
    Was the Manual J presented as part of the contract?
    If yes, put in the right equipment.
    If no, put in the right equipment.
    Designer Dan
    Saint Joseph, MI
    Quote Originally Posted by rickboggs View Post
    or
    I'd use the lower number. Airports tend to be out in the open and at a higher elevation. Unless you on a top of the hill and exposed to the sun, you'll be cooler most of the time.
    I'm for example up on a bluff at a higher elevation that other parts of hte town. On a cool calm winter day, it can be 3-5F cooler at my work which is along the river 150' in elevation lower.