    Mar 2006
    fla
    climate changer w vfd no controler/board
    ok heres the drill guys just put in a dx4 climate changer intertwined coils in the celing,w condensors on the roof. had 2 problems 1 no board or controler (ah540/541)ordered with ahu, any way to make a standard 24v ac multi stage thermostat feed signals to the vfd (would like 2 speeds out of it at least) can probably do it w a couple of relays and and the vfd dc output but hate to get real creative with a new system just yet. and 2, the old piping was semi hermatic 10t w 7/8 liquid line. we reused this for 2 of the 4 circuits, will this subcool too low or still ok, 60-70 ft lineset. new lineset 1/2 X1 3/8 thanks
    Illinois
    What kind of vfd?
    Usually there's a couple contacts for preset speeds. Set those up in the vfd menu, and wire those terminals to a couple ice cubes off your stat or compressors.
    It'll probably work 'til your board shows up. You might have to fiddle with it.
    "If I had my life to live over again, I'd be a KA." - Albert Einstein
    It's later than you think.
    Mar 2006
    fla
    vfd
    I think its danfoss, what ever the optional accessory mfg for the trane climate changer. just hate to rig it dont think the company is gonna buy the board, may just wire it up like a standard full speed ah
    Illinois
    Hold on a minute..
    shouldn't you be running the vfd off a duct pressure sensor?