    What kind of wire is this?

    Coble is marked "P-122 Mesa"

    I think it is a crane cable. 12/4 stranded with thick rubber jacket. It has no other designations, that I can find. I want to use as a 480 volt 3 phase extention cord for 17 ampsload.

  2. #2
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,658
    Post Likes
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  3. #3
    Join Date
    Oct 2002
    Location
    Plano, TX
    Posts
    2,568
    Post Likes
    Thread Starter
    Any NEC reference or manufacturer stuff?

  4. #4
    Join Date
    Aug 2007
    Location
    Northern VA 38 degrees N by 76 degrees W
    Posts
    5,115
    Post Likes
    Quote Originally Posted by timjimbob View Post
    Any NEC reference or manufacturer stuff?
    Your cable would be listed in Article 400 and should have labeling every 24 inches on the surface to indicate the characteristics of the cable.

  5. #5
    Join Date
    Oct 2002
    Location
    Plano, TX
    Posts
    2,568
    Post Likes
    Thread Starter
    No mention of MESA or P122.

  6. #6
    Join Date
    Jul 2000
    Location
    Dallas,Texas
    Posts
    5,155
    Post Likes
    Look again. It is probably P-122 MSHA. (Mine Health Safety Administration) That is an additional rating that is given to cables for durability, flame spread, etc to qualify for use in mines. The same rated cable might be used in a washing machine.
    The NEC does not show any cable assemblies in the #12-4 range that are not rated at least 600 volts.

    http://www.southwire.com/ProductCata...catsheetOEM123

  7. #7
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,658
    Post Likes
    Quote Originally Posted by timjimbob View Post
    No mention of MESA or P122.

    Read the accident report.

    AN EMPLOYEE WAS TROUBLESHOOTING AN ELECTRICAL PROBLEM IN A 2-TON OVERHEAD CRANE. HE WAS USING A MESA EXTENSION CORD SET (TYPE P-122, 4-CONDUCTOR, 600-VOLT, 30-AMPERE).
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  8. #8
    Join Date
    Aug 2007
    Location
    Northern VA 38 degrees N by 76 degrees W
    Posts
    5,115
    Post Likes
    Quote Originally Posted by wolfdog View Post
    Look again. It is probably P-122 MSHA. (Mine Health Safety Administration) That is an additional rating that is given to cables for durability, flame spread, etc to qualify for use in mines. The same rated cable might be used in a washing machine.
    The NEC does not show any cable assemblies in the #12-4 range that are not rated at least 600 volts.

    http://www.southwire.com/ProductCata...catsheetOEM123
    Wolfdog is correct it is MSHA P122 indicates the manufacturer of the cable, and is now owned by Southwire

  9. #9
    Join Date
    Jul 2000
    Location
    Dallas,Texas
    Posts
    5,155
    Post Likes
    Read the report and it should be fairly obvious it was a made up cord set.
    A couple of other things don't add up, like the GFCI extension cord report on a 3 phase 30 amp 600 volt cord.



    P-166 MSHA is a government standard for the mining industry.
    http://www.msha.gov/TECHSUPP/ACC/lists/07cables.pdf

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •