    Need wiring diagram/shotgun for True T-24GC

    Correction- TRUE-The evap fan is not running and it killed the compressor. There is no power to the evap fan and I need to find and verify any components that break the fan circuit. I can't believe how big a pain it is to get to the wiring. You have to take the entire top of the unit off, then you have to remove the entire inside back of the unit apart to get to the wiring. Then you can't really run-test anything because it's apart. Why would a company design a unit that you can remove a few screws to get to the defrost control and then not have enough wiring to pull the control out so you can check the wiring at the terminals????
    Last edited by tcape; 04-01-2013 at 07:20 AM. Reason: Was trying to fix a misspelling in the title
    "Delay is preferable to error"- Thomas Jefferson

  2. #2
    Join Date
    Jul 2000
    Location
    Guayaquil, EC
    Posts
    14,652
    Post Likes
    True doesn't publish wiring diagrams. The best way to get one is to give them a call and they will either fax or email it to you.

    http://www.truemfg.com/24HourTech_en...=401&from=food

    I believe the only control for the evap fan on the glass chillers is the defrost timer, as they don't typically have a fan delay thermostat...but it's best to call. (Have the model & serial number of the box handy.)

  3. #3
    Join Date
    Jan 2008
    Location
    Hanover, PA
    Posts
    317
    Post Likes
    Thread Starter

    Just emailed them, they are sending me the wiring diagram

    Quote Originally Posted by icemeister View Post
    True doesn't publish wiring diagrams. The best way to get one is to give them a call and they will either fax or email it to you.

    http://www.truemfg.com/24HourTech_en...=401&from=food

    I believe the only control for the evap fan on the glass chillers is the defrost timer, as they don't typically have a fan delay thermostat...but it's best to call. (Have the model & serial number of the box handy.)

    Thanks!
    "Delay is preferable to error"- Thomas Jefferson

  4. #4
    Join Date
    May 2013
    Location
    Utah
    Posts
    57
    Post Likes
    AS far as " True " I would go with the shotgun approach.
    They are " Truly " infuriating to work on.
    They sent a number of boxes out which " by their design " cycled the evaporator fan with the compressor.
    The KM said " This box has never worked right since it was new...."
    When I asked the Engineering rep at True why they did this he said it was for " efficiency."
    I'm not sure why they think they can run refrigeration like an air conditioner????
    I had to just hang up the phone and laugh silently about the whole affair after wiring the unit correctly.
    I have seen VERY large building mechanical systems that were also just as badly engineered totally self destruct.
    All Mechanics at large need to whenever possible, start questioning Engineers and do everything possible to hold them accountable for what they put out there.

    Sincerely

  5. #5
    Join Date
    Oct 2008
    Location
    In a kitchen with my head stuck in an oven
    Posts
    1,659
    Post Likes
    Quote Originally Posted by tcape View Post
    ...Why would a company design a unit that you can remove a few screws to get to the defrost control and then not have enough wiring to pull the control out so you can check the wiring at the terminals????
    Same folks that run a lineset up through the back wall. Then, if you gotta a clogged capillary, they sell you an externally mounted channeled kit to route the "replaced" capillary.
    Hey - they're the epitome of commercial equipment...so a problem is rare...

    Quote Originally Posted by StarCat View Post
    When I asked the Engineering rep at True why they did this he said it was for " efficiency."
    Hence, their new buzzword in that they're "going green" with natural, low ODS refrigerants.

  6. #6
    Join Date
    Oct 2008
    Location
    In a kitchen with my head stuck in an oven
    Posts
    1,659
    Post Likes
    I forgot to mention: True may put thier diagrams in some obscure locations. Their upright two-door units, it's behind the louvered kick panel on the backside of the center channel cover where the condenser plugs into. If memory serves, there's another upright unit that has a metal box next to the condenser that encloses the their defrost timer and other electrical stuff. A side cover comes off of that and may have a diagram. I don't have a clue about this chest freezer "glass froster" you're looking at. Never seen one.

  7. #7
    Join Date
    Oct 2009
    Location
    Raleigh, NC
    Posts
    1,022
    Post Likes
    Remember that there are a LOT of True units running out there. For every one you work on there are 20 more that run for years and years with very little service.

    Regarding cap tubes in True units...Has anyone ever had much luck running a replacement tube up through the suction line? I think most techs that were told to try this gave it a whirl and didn't have any success. I have done it several times without too much trouble.

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •