Keep looking, www.bpi.org www.comfortinstitute.org
The Carrier guy said he doesn't need to know any of that information and I was looking to install a greenspeed. all he said to me was he recommends a performance model and it is more common. he asked me to send him the house plans.
The Whestinghouse said I needed a 3 ton without a load cals.
I cant get a response from anyone when I ask them to do a load cals.
What do I do when I can't install it myself.
I know I need a 2 ton for cooling and a 2 ton for heating, I would like to have a 2.5 ton for heating in the northing environment.
I have a heat gain of 21475 and a heat loss of 24672. this is baesd on 7 degrees. so a 2 ton is all I need.
Everyone here seems to go by rule of thumb.
Jimmy
Keep looking, www.bpi.org www.comfortinstitute.org
Fly me up, I'll do it for 10x what I would normally get for a 2 ton inverter drive heat pump and duct system...lol Just keep looking and demand a load calc etc. I'm guessing there is no one in your area on the contractor locator on this site or the ones I linked or www.resnet.us www.natex.org
Also go here. https://www.acca.org/consumer/find-a-contractor/
I'm flying to Arlington VA on Monday to spend a week with Hank R the author of Manual J to be certifided as an instructor in the ACCA manuals.
Make your expertise uniquely valuable.
Make your influence uniquely far-reaching.
I would like to think there are alot of qualified and good HVAC people here I think they use ROT more than necessary
I should say use the ROT more than they should or never use it at all
Find out who the local distributor is of your desired equipment and call them, explaining that you would like a dealer that will do a Manual J. Or if they would be able to complete one on your home.
Make your expertise uniquely valuable.
Make your influence uniquely far-reaching.
There buying the equipment from a distributor, do a little on line research and find there source.
Make your expertise uniquely valuable.
Make your influence uniquely far-reaching.
Keep looking
Make your expertise uniquely valuable.
Make your influence uniquely far-reaching.
I know what I want. I have the load calc done and I would like the york YHJF 2.5 or the Trane 15 2.5
It is frustrating when no one answers phones or e-mails. Guess they are to busy and don't need my buisness.
I know pricing isn't allowed but I could buy a nice new car for what they wanted for a westinghouse 3 ton and he didn't even see my place
Designer Dan __ It's Not Rocket Science, But It is SCIENCE with Some Art. _ _ KEEP IT SIMPLE & SINCERE ___ __ www.mysimplifiedhvac.com ___ __ Define the Building Envelope & Perform a Detailed Load Calc: It's ALL About Windows & Make-up Air Requirements. Know Your Equipment Capabilities
Page 9 for heating capacities
2.5 ton
47'F 30,000 btu/hr
17'F 18,700 btu/hr
http://www.upgnet.com/PdfFileRedirec...ytg-c-1211.pdf
Designer Dan __ It's Not Rocket Science, But It is SCIENCE with Some Art. _ _ KEEP IT SIMPLE & SINCERE ___ __ www.mysimplifiedhvac.com ___ __ Define the Building Envelope & Perform a Detailed Load Calc: It's ALL About Windows & Make-up Air Requirements. Know Your Equipment Capabilities
Try Mat at Aire Serv.
I would think he would be able to handle this request.
Quality and Value Service and Repair
I could get away with the 2 ton and Aux heat.
I re did all my Load calc's and I now have 24067 cooling and 24166 heating @ 10 degFfor winter and 85 for summer . A inside temp of 72 in winter and 77 in summer.
I have someone coming to do load calc and give me an estimate, within the next week They do mostly industrial refrigeration but also do residential HVAC. They said they can install almost any product that I want. The do a fair amount of the Mitsubishi Zuba that I had never heard of but I have read some good things about them here. Though It may be too large for my needs.
Jimmy
Last edited by JimmyP; 04-01-2013 at 10:42 PM. Reason: spelling