    Reversing valve or txv

    Diagnosing a Trane 5ton packaged heat pump Suction pressure will not go above 60. Reversing valve very sluggish furring changeover. Any thoughts

  2. #2
    Join Date
    Jun 2005
    Location
    SW Wisconsin
    Posts
    4,451
    Quote Originally Posted by Spider-man View Post
    Diagnosing a Trane 5ton packaged heat pump Suction pressure will not go above 60. Reversing valve very sluggish furring changeover. Any thoughts
    With a 5-Ton heat pump there may not be enough airflow heatload to load the coil & suction pressure above 60-psig.

    Also, could be somewhat low on refrigerant.

    There are a number of components in the refrigerant system; besides the TXV & reversing valve; that need checking.

    The systems airflow should be checked first, then subcooling & superheat should be checked.
    Also, check the temperature rise off the outdoor unit & the temp-drop indoors between Return air & supply air, along with the % of relative humidity; the indoor humidity level is critical to know when trouble shooting a system.

    All the system pressures need to be checked...

    Some indicators will begin to show-up.