    NV Alarm

    Got a old Lonspec project that we are bringing into a Jace. Mostly xl10's with 1 xl15a and 3 xl15c's. All the xl10's are good and I ripped out the xl15a(replaced with a Spyder). The xl15c's were a mess. The programming was broken before we even brought them in. I ended up redoing the programming from scratch.

    Well the problem is......the controllers are in alarm. It's Input_NV_Alarm. Spent a couple hours going through all my points and can't figure out what the problem is. As far as bindings.....all proxy bindings, with the exception of OA temp and humid coming into the controllers on a Network Input block and terminal load and avg space temp coming in on a remote ai block.

    Any ideas?

  2. #2
    Join Date
    Feb 2013
    Location
    Phoenix, AZ
    Posts
    198
    Is that the actual name of the nv? I have a listing of XL10 nv's, and they all start with the usual nvi, nvo, nci. I don't find one that resembles Input_NV_Alarm. Are they VAVI, VAVII, CVAHU controllers, or what?

  3. #3
    Join Date
    Jun 2006
    Location
    New Jersey
    Posts
    4,340
    Input_NV_Alarm is the name of the controller alarm. These a xl15c's.

    The alarm definition from Honeywell- "One or more network variable (NV) inputs have failed in receiving an update within their specified FAILURE_DETECT_TIME. This is valid only on those NVs with fail detect."

  4. #4
    Join Date
    Feb 2013
    Location
    Phoenix, AZ
    Posts
    198
    Ah - when you said mostly XL10's I assumed the alarm was coming from them. I was looking in the wrong place.