    Buderas oil to gas

    Customer has a Buderus G215/5 238mbtu/hr boiler. Wants to convert to natural gas because their running a line by his house.
    Oil burner now is a Riello 40 F10 1.45 firing rate. He has a 1.25 Nozzle in it now.
    Any reccomendations.

    Also I want to us TracPipe Counterstrike. I have been doing all black iron. Where is the requirement for bonding. Is there any advantage to using the "T",s as opposed to a IPS end and a iron "T".

  2. #2
    Join Date
    Aug 2001
    Location
    Pavilion, NY
    Posts
    2,139
    Riello conversion gas burner would be perfect. As for the Csst piping,,, #6 copper needs to be run from a bonding clamp at the closest point of entry black pipe into the building to the panel.
    ...

  3. #3
    Join Date
    Jan 2012
    Location
    Broomall, PA
    Posts
    397
    X2, call Riello tech support for proper sizing. 1 800-4-RIELLO

  4. #4
    Join Date
    Feb 2012
    Location
    Maine
    Posts
    23
    Thanks