    Transformer amp rating

    I need to install a transformer to power a Enclosure A/C unit. The unit is rated at 9.0 FLA. I have a transformer that is 1 phase, 460 V Primary, 120 V Secondary and 2 KVA. I think this would equal 16.6 amps, am I correct with my figures?

  2. #2
    Join Date
    Feb 2007
    Location
    Central NJ
    Posts
    570
    Post Likes
    So your looking for transformer VA? Multiply secondary side volts by amps, that will give you required transformer VA.

  3. #3
    Join Date
    Feb 2013
    Location
    Phoenix, AZ
    Posts
    198
    Post Likes
    You are correct, a 2 KVA transformer with a 120V secondary will supply 16.6A to the load.

  4. #4
    Join Date
    Sep 2006
    Location
    Ohio
    Posts
    517
    Post Likes
    Quote Originally Posted by DDC_Dan View Post
    You are correct, a 2 KVA transformer with a 120V secondary will supply 16.6A to the load.
    Thanks for the reply, I just wanted to make sure I was right.