    Transformer amp rating

    I need to install a transformer to power a Enclosure A/C unit. The unit is rated at 9.0 FLA. I have a transformer that is 1 phase, 460 V Primary, 120 V Secondary and 2 KVA. I think this would equal 16.6 amps, am I correct with my figures?

  2. #2
    Join Date
    Feb 2007
    Location
    Central NJ
    Posts
    506
    So your looking for transformer VA? Multiply secondary side volts by amps, that will give you required transformer VA.

  3. #3
    Join Date
    Feb 2013
    Location
    Phoenix, AZ
    Posts
    198
    You are correct, a 2 KVA transformer with a 120V secondary will supply 16.6A to the load.

  4. #4
    Join Date
    Sep 2006
    Location
    Ohio
    Posts
    473
    Quote Originally Posted by DDC_Dan View Post
    You are correct, a 2 KVA transformer with a 120V secondary will supply 16.6A to the load.
    Thanks for the reply, I just wanted to make sure I was right.