    Quote Originally Posted by small change View Post

    The ecm motor will fail if the filter isn't maintained regularly and properly
    And where did you get this information?

  2. #15
    Join Date
    Mar 2013
    Posts
    8
    Quote Originally Posted by small change View Post
    specify what model number/brand of condensate pump to be installed instead of heavy duty (nitpicking)

    Refrigerant piping Usually equals Lineset and in a lineset the suction line comes preinsulated liquid line does not. is this the case?

    Raintight disconnect box....no mention of a fusible disconnect which it should be.

    No mention of Permit...permit costs costs or the pulling of a permit with the local jurisdiction.

    Why an 80% why not a 90%? Where are you located?
    Thanks for feedback small change. Is 90% more edficient? Located in NJ.

  3. #16
    Join Date
    Sep 2003
    Posts
    1,677
    Quote Originally Posted by pecmsg View Post
    And where did you get this information?
    Perhaps I should have said Scheduled, Regular maintenance on your furnace will keep it running
    efficiently for a long time.

    But I have been running into a spate of ecm motors (modules) lately that have failed due to poor maintenance practices and the direct correlation was a failure to change the filter media for sometimes years at a time.

    I suppose the same could be said for any furnace/motor combination with an extremely dirty filter but just something I have run into lately.

  4. #17
    Join Date
    Sep 2003
    Posts
    1,677
    Yes 90% furnace is more efficient than an 80% effiicent.

    Ask any contractor to quote you both if he is just quoting you an 80%

  5. #18
    Join Date
    Feb 2009
    Location
    Tallahassee, FL
    Posts
    6,051
    How big is your house and how did they determine what size you needed. The posted sizes would typically be a 3000+ sq ft home.

  6. #19
    Join Date
    Mar 2013
    Posts
    8
    House is about 2400 sq ft (1200 sq ft per floor).
    Also have finished attic which will not be hvac-equipped.
    Live in NJ, gets cold in winter and quite humid an summer.

Page 2 of 2 FirstFirst 12

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event