    I need a little advice on which way to proceed with a new system.

    I’m looking to have both the furnace and central A/C replaced in my house. The system is 18 years old and has worked fine but the A/C is starting to make me nervous. It seems to run for longer periods at a time and the electric bill is reflecting this.

    My only complaint with the old system is I think it could dehumidify better on moderate days. The house is 2850 sq ft, with about 1350 of that being finished walkout basement. On days when the furnace is not running or the A/C is not on for extended periods of time the air feels clammy. Also, I think a two stage furnace would be nice for better winter comfort.

    I’ve had three contractors submit bids for the work. I’ll list the specifics below:

    Dwelling: 1500 sq ft Main floor, 1350 sq ft walkout basement. About 100ft of wall below grade. Well insulated and newer windows. Eight foot ceilings.

    Current System:
    Trane 92% 80K BTU Furnace Single-Stage
    Trane XE1000 2.5 Ton AC Single-Stage


    Contractor #1: A little concerned that the AC would not run on the high stage much.

    Load Calc
    Heating:78,000
    Cooling: 29,500

    Proposed Equip:
    Heating: 80K, 96% 2-stage, variable speed.
    Cooling: 3 Ton, 2-stage

    Contractor #2: Concerned that on the hottest days, the unit would not keep up, but would dehumidify very nicely.

    Load Calc
    Heating: 75,900
    Cooling: 27,000

    Proposed Equip:
    Heating: 85K, 95% 2-stage
    Cooling: 2 Ton, 2-stage

    Contractor #3

    No Load Calc. Based on lengthy conversation and performance of old system recommended the following:

    Proposed Equip:
    Heating: 80K, 95% 2-stage
    Cooling: 2.5 Ton single stage.

    I appreciate any input you experts care to offer. Also, I'm an electrical engineer with a passion for home automation and AV systems. I'm happy to help any of you that I can with my expertise.

    Thank you.

  2. #2
    Join Date
    May 2008
    Location
    Missouri
    Posts
    4,384
    Post Likes
    Lord....your home has a 70,000 BTU heat loss????? Wow, since it sounds like it's about a 1500 sq. ft home with most of basement finished. I'm assuming someone has actually done a manual J to confirm this? Short cycling a 95% furnace due to oversizing will result in a very poor efficiency and short life. What are the manual J figures on heat loss and gain?

  3. #3
    Join Date
    Mar 2013
    Posts
    13
    Post Likes
    Thread Starter
    Quote Originally Posted by wahoo View Post
    Lord....your home has a 70,000 BTU heat loss????? Wow, since it sounds like it's about a 1500 sq. ft home with most of basement finished. I'm assuming someone has actually done a manual J to confirm this? Short cycling a 95% furnace due to oversizing will result in a very poor efficiency and short life. What are the manual J figures on heat loss and gain?
    OK, I'll need to talk these guys and see what the manual J figures are, assuming that's how they figured it. I think the BTU's that I listed were the required BTU's that the equipment would need to be capable of. But really, my biggest question is related to cooling and the fact that the current 2.5 TON seems to be sufficiently sized. And if I were to go 2-stage they are telling me that you either round up to 3 TON or round down to 2 TON.

    Two TON seems a little light, but three TON might not ever operate in the high stage and would be a waste of money.

  4. #4
    Join Date
    May 2008
    Location
    Missouri
    Posts
    4,384
    Post Likes
    I'd have (or simply do) a manual J heat loss/gain computation, and then start from there. If you want better dehumidification, the LAST thing you want is to oversize the cooling unit. Maybe look into the two ton two stage with optional dehumidifier! But I'd get some idea of what you really need first as the older 2 1 /2 ton unit may have been too large and shutting off too much. You won't dehumidify if the unit is shutting off in hot high humidity weather.

  5. #5
    Join Date
    May 2000
    Location
    Indianapolis, IN, USA
    Posts
    42,886
    Post Likes
    On days when the furnace is not running or the A/C is not on for extended periods of time the air feels clammy.
    A bigger or 2 stage A/C won't help this. Best bet is a whole house dehumidifier, especially since you have the large basement which is 40% or so of your total sq ft. This area has little sensible heat gain adding to the A/C needs but does at a lot of latent. Personally I'd go with a good single stage A/C with a good latent capacity and a good dehumidifier. Can be tied in to the duct system or just dry the basement which will lower the humidity in the entire house. Many are ventilating to bring in and dry outside air freshening the place.

    I'm with the others questioning the 80K 95% furnace. The insulated basement will not add that much to the whole house heat needs. Of course if you are in a very northern, cold climate, you might need all that heat. Don't think I saw anywhere your location.

  6. #6
    Join Date
    Mar 2013
    Posts
    13
    Post Likes
    Thread Starter
    Northern Indiana, lakefront with a lot of windows facing the north.

  7. #7
    Join Date
    Jul 2006
    Location
    Prata di Pordenone Italy
    Posts
    8,069
    Post Likes
    a trane 3 ton 20i would do it 1.5 ton in first stage 3 ton in second stage

  8. #8
    Join Date
    Jan 2009
    Location
    SE Iowa
    Posts
    5,577
    Post Likes
    I'm wiht others. 60k and 2 tons should be plenty since most windows face north. The lake will also temper summertimes temps, but can raise humidty, especially at night. A 2 tosn 2 stage might help that clmminess, but as mentoned, a ventilating dehumidifier will work best... and with a whole house dehumidifier, it shifts load off the AC so a 2 ton will easily hold the load in a house that size.

  9. #9
    Join Date
    Mar 2013
    Posts
    13
    Post Likes
    Thread Starter
    Thanks for the all replies. I did talk to my contractors about their calculations and come to find out, I'm a little disappointed. Contractor #1 who claims to be Trane's highest volume and most awarded dealer in the Northern Indiana area, simply used data from a website that utilizes Google Earth.

    Contractor #2 couldn't tell me the name of the program he used, actually his daughter who works in the office does the load calcs. But at this point, I'll give him credit for having something.

    I ended up buying the residential version of Don Sleeth's HVAC-calc and here is what it is telling me.

    Design criteria

    Outside Temp: 100 degrees
    Inside Temp: 75 degrees

    Heat Gain: 25,262
    Sensible: 22,863
    Latent: 2,399

    So, based on this info, is a 2 ton sufficient?

    Thanks again.

  10. #10
    Join Date
    Mar 2013
    Posts
    13
    Post Likes
    Thread Starter
    Actually, here is the report.

    Name:  Load Calc.jpg
Views: 198
Size:  51.0 KB

  11. #11
    Join Date
    Mar 2013
    Posts
    13
    Post Likes
    Thread Starter
    Name:  Load Calc.jpg
Views: 198
Size:  53.0 KB

  12. #12
    Join Date
    Jun 2003
    Location
    Madison, WI/Cape Coral, FL
    Posts
    12,042
    Post Likes
    Looking over the load calcs, the latent load is lower than I would have expected. ASHRAE suggest 500 btus of latent load per occupant. A home your size, should have a fresh air change in 4-5 hours. This is an additional 3,000 btus of latent load. Also consider that the latent loads are independent of the sensible cooling loads. That is the reason that the home is damp when there is low/no cooling loads. Without a significant cooling load, even a two speed a/c is unable to remove 2,000-4,000 btus of latent cooling load. With a naturally cool basement space, expect the home to be clammy at best. After a couple months of +65%RH, basements smell like basements and dust mites grow in bedding and favorite furniture.
    To maintain <50%RH throughout the home and get adequate fresh air change, adding a whole house to a good basic a/c with keep the home at <50%RH and fresh air throughout. Now for the commercial, check out the Ultra-Aire whole house dehu, a sponsor of the site. There are other brands also. A 3 pint per hour dehu is minimum for your application.
    Keep us posted.
    Regards TB
    Bear Rules: Keep our home <50% RH summer, controls mites/mold and very comfortable.
    Provide 60-100 cfm of fresh air when occupied to purge indoor pollutants and keep window dry during cold weather. T-stat setup/setback +8 hrs. saves energy
    Use +Merv 10 air filter. -Don't forget the "Golden Rule"

  13. #13
    Join Date
    Jan 2009
    Location
    SE Iowa
    Posts
    5,577
    Post Likes
    Quote Originally Posted by lakebilly View Post
    Actually, here is the report.

    Name:  Load Calc.jpg
Views: 198
Size:  51.0 KB
    Here's a good example of gigo (garbage on garbage out) summer design temp I'd NOT 100f. Only parts of Texas and az hold that distinction. Out only 87 for Valpo with a fairly humid 74f wet bulb. I Bet 100 had only happened 4 or 5 days since 1940 and your record is like 105. In comparison, out hot 100 or higher here i think 3 times last summer and in places like Texas, it a normal occurance mid summer

    Sent from my DROID RAZR using Tapatalk 2

  14. #14
    Join Date
    Mar 2013
    Posts
    13
    Post Likes
    Thread Starter
    Quote Originally Posted by motoguy128 View Post
    Here's a good example of gigo (garbage on garbage out) summer design temp I'd NOT 100f. Only parts of Texas and az hold that distinction. Out only 87 for Valpo with a fairly humid 74f wet bulb. I Bet 100 had only happened 4 or 5 days since 1940 and your record is like 105. In comparison, out hot 100 or higher here i think 3 times last summer and in places like Texas, it a normal occurance mid summer

    Sent from my DROID RAZR using Tapatalk 2
    Actually, HVAC-calc defaults to a higher outside than 100, can't remember exactly, but I did back it down. Fort Wayne and Valpo are very similar in weather. What would you recommend for an Outside Temp?

  15. #15
    Join Date
    Jul 2006
    Posts
    1,091
    Post Likes
    motoguy128 is right,
    I don't know about the default but, HVAC-Calc Res has South Bend and Goshen at 89db summer and 1db winter, Valp is 90dp and 3db. WrightJ has South Bent at 91summer and 5 winter.

  16. #16
    Join Date
    Jan 2009
    Location
    SE Iowa
    Posts
    5,577
    Post Likes
    Oh... and you winter temp for Valpo is 3F. Right on the lake it's probably higher, 4-5F.

    Fort Wayne is quite a bit inland, according to the official statistical data, it's lower as you go north and closer to te lake. Large bodies of water ALWAYS have a tempering effect. Not only the water itself, but the lake effect clouds and precipitation.

    Even where I am, the Mississippi river is about 1/2-3/4 mile wide and has a slight tempering effect at times. Depending on wind direction I can also get slightly higher humidity. Compounding that I'm up high on a bluff and in calm winds, it can be 3-5F difference from along the river where my work is to my house 300' higher only 2 miles away. Cold air falls & warm air rises.

  17. #17
    Join Date
    Mar 2013
    Posts
    13
    Post Likes
    Thread Starter
    Quote Originally Posted by teddy bear View Post
    Looking over the load calcs, the latent load is lower than I would have expected. ASHRAE suggest 500 btus of latent load per occupant. A home your size, should have a fresh air change in 4-5 hours. This is an additional 3,000 btus of latent load. Also consider that the latent loads are independent of the sensible cooling loads. That is the reason that the home is damp when there is low/no cooling loads. Without a significant cooling load, even a two speed a/c is unable to remove 2,000-4,000 btus of latent cooling load. With a naturally cool basement space, expect the home to be clammy at best. After a couple months of +65%RH, basements smell like basements and dust mites grow in bedding and favorite furniture.
    To maintain <50%RH throughout the home and get adequate fresh air change, adding a whole house to a good basic a/c with keep the home at <50%RH and fresh air throughout. Now for the commercial, check out the Ultra-Aire whole house dehu, a sponsor of the site. There are other brands also. A 3 pint per hour dehu is minimum for your application.
    Keep us posted.
    Regards TB
    Thanks TB

    I will give the whole house dehumidifier some very serious consideration. That will put me well over budget, but after reading some of your other posts on the subject, it might be best if I were to drop back to a single stage AC and put some money toward a WH dehumidifier. I read somewhere that Honeywell makes the quietest unit available. That will be very important because the utility room where it will be housed is adjacent to the family room where we watch TV. What would you compare the noise level of one of these units too?

    One other question. If my sensible heat gain is 22,863 and latent is: 2,399 is a 2 ton unit sufficient? The AHRI ratings of the proposed condenser/coil combination is 23,600 total and 16,100 sensible.

    Thanks again.

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •