    Goodman HP sounds like airplane in defrost

    CPLE24-1C

    I've read long ago about units sounding like this , and think it was typically normal

    But I thought I'd make sure

    Its my dads house he just purchased , and he says it sounds like a jet landing when going into defrost

    Works fine otherwise

  2. #2
    Join Date
    May 2009
    Location
    Savannah, Ga/H.H. Island, S.C.
    Posts
    1,277
    If the system isn't equipt with quiet shift....I would add the relays to allow the ODU to shut down during switchover to defrost.

    I checked your profile and found no email. Email or PM me and I will send you a step by step wiring diagram to install the proper relays for quiet shift.

  3. #3
    Join Date
    Apr 2004
    Location
    MN
    Posts
    1,781
    Brent, I would like to see those diagrams. Email in my profile. Thanks
    A Veteran is a person, who at some point in their life, wrote a blank check payable to the United States of America for payment up to and including their life.
    Gene Castagnetti-Director of the National Memorial Cemetery of the Pacific in Hawaii

  4. #4
    Join Date
    May 2009
    Location
    Savannah, Ga/H.H. Island, S.C.
    Posts
    1,277
    Just sent it Doc.

  5. #5
    Join Date
    May 2005
    Location
    South Carolina
    Posts
    61
    Brent, I would also like to see those diagrams. Email in my profile. Thank You

  6. #6
    Join Date
    May 2009
    Location
    Savannah, Ga/H.H. Island, S.C.
    Posts
    1,277
    Just sent Augie.

  7. #7
    Join Date
    Apr 2004
    Location
    MN
    Posts
    1,781
    Thanks Brent! And thanks to Rundawg!
    A Veteran is a person, who at some point in their life, wrote a blank check payable to the United States of America for payment up to and including their life.
    Gene Castagnetti-Director of the National Memorial Cemetery of the Pacific in Hawaii

  8. #8
    Join Date
    Jul 2009
    Location
    South Carolina
    Posts
    2,857
    Before changing the defrost to a soft start on that unit I would want to be 100% sure the RV is causing a problem during defrost & not the termination stat causing the head to go too high. That is an older 10 SEER & I'm pretty sure with a recip compressor & no factory hard start components. Of course the hard start can be easily added but I would manually shift the unit into defrost by shutting off the power to the condenser, jumping the RV into cooling mode & unplugging the fan & then putting the power back to it real fast just like it would happen on a soft defrost cycle. That would confirm whether the soft start defrost would solve your problem or not.
    Gary
    -----------
    http://www.oceanhvac.com
    An engineer designs what he would never work on.
    A technician works on what he would never design.