    Went to a service call where the customer complained about their walk-in cooler not cooling. Upon arrival, hooked up gauges and noted very low pressures. Furthermore, I could hear a tiny hissing noise coming from somewhere behind the compressor along the back wall. I finally found this on the 1/4" liquid line (against the wall)...not quite sure how this would happen?

    Name:  Pipe leak.jpg
Views: 1058
Size:  13.8 KB

    Anyways, cut out the section of copper and brazed connection...pressurized with nitro, checked for leaks, evacuated and charged...problem solved.

  2. #2
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,690
    Post Likes
    Vibration and abrasion.



  3. #3
    Join Date
    Mar 2009
    Location
    Mid-Mo
    Posts
    3,600
    Post Likes
    Quote Originally Posted by jpsmith1cm View Post
    Vibration and abrasion.


    You could have probably fixed that?

  4. #4
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    23,572
    Post Likes
    Not all that uncommon
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Why is it that those who complain the most contribute the least?
    MONEY CAN'T BUY HAPPINESS. POVERTY CAN'T BUY ANYTHING

  5. #5
    Join Date
    Feb 2013
    Location
    Vancouver, BC
    Posts
    16
    Post Likes
    Thread Starter
    I see..that makes sense. This was the first time I came across this type of problem...and didn't realize this was common.

    Quote Originally Posted by ryan1088 View Post


    You could have probably fixed that?
    Maybe I could have brazed that section, if thats what you mean by fix, but there was about 2" of thinned out wall. It made more sense to me to cut out the piece...cleaner, quicker and used less silfos.

    What you all think, cut & braze or just braze?

    Sent from my SGH-I747M using Tapatalk 2

  6. #6
    Join Date
    Feb 2006
    Location
    USA
    Posts
    4,381
    Post Likes
    I would of brazed it

    Sent from my SGH-T999 using Tapatalk 2

  7. #7
    Join Date
    May 2009
    Location
    The Pas, Manitoba Canada
    Posts
    236
    Post Likes
    The pipe was rubbing against something if it could slide or something was rubbing against the pipe. Watch out for doors being propped up against it etc. Should be able to see same kind of markings on what caused the problem.

  8. #8
    Join Date
    Mar 2009
    Location
    Mid-Mo
    Posts
    3,600
    Post Likes
    I would have fixed it in place also.

  9. #9
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    23,572
    Post Likes
    OP, It's common where linesets are not properly secured. Many times when the LLS energizes, the initial jolt of refrigerant going thru the line will cause a vibration.Also common when installers use use precharged linesets and stack the leftover coils on the roofs, on top of the box, or in the celing.
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Why is it that those who complain the most contribute the least?
    MONEY CAN'T BUY HAPPINESS. POVERTY CAN'T BUY ANYTHING

  10. #10
    Join Date
    Jul 2012
    Location
    Western KY
    Posts
    1,221
    Post Likes
    I would have cut it out, in most cases, not much more time to do and just looks better. I have fixed them in place with equal success, 100 degrees and 5 calls waiting, but prefer to cut them out. That's just me though. Both are fine.

  11. #11
    Join Date
    May 2010
    Location
    Brooklyn, NY
    Posts
    99
    Post Likes
    it's a very very rare case, even if the lines are not properly secured to the wall or other stuff around, the vibration shouldn't be strong enough to cause such an abrasion from over time. I would say the lines they used when it was installed were already damage in that portion, and with overtime abrasion, it rubbed out a hole. But yea for better result, I would cut it, although that takes alot more time when you have to vacuum, and recharge the system

  12. #12
    Join Date
    Mar 2013
    Posts
    44
    Post Likes
    Usually get stuff like that on distributor tubing rubbing up on one if the rungs or some nonsense. Don't see it happen on a wall often... I'd have patched too tho. Quick pump down, drier swap, patch, open receiver valve and let her rip. 15 minute fix.

  13. #13
    Join Date
    Sep 2006
    Location
    Chicago
    Posts
    491
    Post Likes
    You did the right thing. Only takes a few more minutes to cut it out and replace it. I've been on a few calls working on roofs in -20 temps and 40mph winds where someone brazed over the rub through and it leaked out the blob of weld again 2 years later. Of course at the worst time.

  14. #14
    Join Date
    Oct 2009
    Location
    Raleigh, NC
    Posts
    1,022
    Post Likes
    Quote Originally Posted by EEAllen View Post
    it's a very very rare case, even if the lines are not properly secured to the wall or other stuff around, the vibration shouldn't be strong enough to cause such an abrasion from over time.
    I strongly disagree! I had THREE rubthroughs last week on different condensing units (main piping), and TWO pressure control lines rubbed through. Yesterday I found a Lennox L-series where the discharge line from stage one compressor rubbed through on the tail of the crankcase heater worm clamp from the stage 2 compressor. I also had an evap fan wire in a unit cooler that had rubbed through and shorted.

  15. #15
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    23,572
    Post Likes
    Quote Originally Posted by MicahWes View Post
    I strongly disagree! I had THREE rubthroughs last week on different condensing units (main piping), and TWO pressure control lines rubbed through. Yesterday I found a Lennox L-series where the discharge line from stage one compressor rubbed through on the tail of the crankcase heater worm clamp from the stage 2 compressor. I also had an evap fan wire in a unit cooler that had rubbed through and shorted.
    If you read the rest of the post you quoted, it appears he doesn't like to pull vacuums either
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Why is it that those who complain the most contribute the least?
    MONEY CAN'T BUY HAPPINESS. POVERTY CAN'T BUY ANYTHING

  16. #16
    Join Date
    Jul 2012
    Location
    Western KY
    Posts
    1,221
    Post Likes
    Quote Originally Posted by EEAllen View Post
    it's a very very rare case, even if the lines are not properly secured to the wall or other stuff around, the vibration shouldn't be strong enough to cause such an abrasion from over time. I would say the lines they used when it was installed were already damage in that portion, and with overtime abrasion, it rubbed out a hole. But yea for better result, I would cut it, although that takes alot more time when you have to vacuum, and recharge the system
    :0

  17. #17
    Join Date
    Jul 2012
    Location
    North west Arkansas
    Posts
    86
    Post Likes
    Quote Originally Posted by 2sac View Post
    OP, It's common where linesets are not properly secured. Many times when the LLS energizes, the initial jolt of refrigerant going thru the line will cause a vibration.Also common when installers use use precharged linesets and stack the leftover coils on the roofs, on top of the box, or in the celing.
    Yep, seen precharged line sets just hanging still coiled above ceiling, coiled line rubbing against itself.

  18. #18
    Join Date
    Jan 2007
    Location
    Pittsburgh
    Posts
    183
    Post Likes
    Yep see that alot...sometimes not easy to find..

  19. #19
    Join Date
    Oct 2008
    Location
    In a kitchen with my head stuck in an oven
    Posts
    1,659
    Post Likes
    Quote Originally Posted by coolerguy View Post
    Yep see that alot...sometimes not easy to find..
    Yup... like the lineset I had in a Jim 'n Nick's, suspended between top of W/I and roof of building (the attic) in a coil - accessible ONLY by ladder through the ONLY possible ceiling tile that could get me there - above another W/I's door they could only NOT use at 6am - an hour before the crew came in.
    .
    Once up there, access required traversing, ducking & crawling by flashlight through something worse than a typical attic for about 30'.

    Got to the coiled & dangling copper tubing of a system installed only a month ago, to find the lineset virtually rubbed right through each other.

    I (or my company) didn't do it.

    That lineset was worthy of a Wall of Shame post.

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •