Results 1 to 13 of 13
    NE OHIO
    Goodman furnace not draining
    Working on a 2 year old GMS90703BXA, condensate will not drain while its running. Shut it off it'll drain. Nothing is plugged.
    5,000 ft
    #1. Remove Goodboy equipment.
    #2. Discard in trash receptacle.
    #3. Install professional brand equipment.
    Nov 2001
    east kansas
    Loosing negative pressure on the inducer suction side. Could be cracked trap or bad collector box seal. Have to call a pro and even at that it may be hard for an experience guy to find right away.
    Dec 2006
    Middle Tennessee
    Quote Originally Posted by steve3871m View Post
    what equipment do you prefer?
    does this mean you wont fix anything unless it is your favorite equipment?
    Dec 2006
    Middle Tennessee
    Quote Originally Posted by youngtech View Post
    for starters, i would at least make sure the trap had water in it!
    Dec 2003
    Location!, Location!
    A qualified tech should check all the hoses, fittings, and trap. If that's you-register as pro.
    NE OHIO
    Quote Originally Posted by rimek View Post
    in process of doing just that
    NE OHIO
    Quote Originally Posted by Airmechanical View Post
    it does have water in it, first time i ever saw a trap like this. It is open at the top, you can look right in it
    Dec 2003
    Yes it is-don't be scared- check all the other things mentioned.
    Nov 2001
    east kansas
    Check to make sure all the condensate lines are in their proper position. Have to get the book out for this one.
    Dec 2006
    Goodman
    You are lucky if that is the only problem you have with the Goodman. Don't worry you will get to change the fan relay soon.
    california
    make sure drain system is setup correctly
    trap set is correctly configure
    check for air leak
    Urbandale IA. USA
    Do you have pictures you could post?
    If any one shortened the plastic pipes that stick down into the trap, it will change the characteristics of the trap.
    The top of the trap MUST be lower than 2" below the hole in the side of the furnace for the drain to work properly.
    Does it drain with the top access pannel removed? If it does, you could have a combustion air supply problem.
    Measure the static pressure at the collection box cover drain with a mannometer to see what the inducer is doing.
    For MOST brands the inducer will pull 2" wc and therefore the trap must be lower than 2" below the lowest condensing tap....
    Ignore those who belittle Goodman, they are jellous that they cannot compete with price and generaly repair the ones that have been improperly installed in the first place...
    Those who dance, appear insane to those who do not hear the music.
    Those who believe, appear ignorant to those who do not know God.