    Goodman furnace not draining

    Working on a 2 year old GMS90703BXA, condensate will not drain while its running. Shut it off it'll drain. Nothing is plugged.

  2. #2
    Join Date
    Mar 2005
    Location
    5,000 ft
    Posts
    2,224
    #1. Remove Goodboy equipment.
    #2. Discard in trash receptacle.
    #3. Install professional brand equipment.
    Last edited by steve3871m; 01-28-2007 at 03:00 AM.

  3. #3
    Join Date
    Nov 2001
    Location
    east kansas
    Posts
    8,038
    Loosing negative pressure on the inducer suction side. Could be cracked trap or bad collector box seal. Have to call a pro and even at that it may be hard for an experience guy to find right away.

  4. #4
    Join Date
    Dec 2006
    Location
    Middle Tennessee
    Posts
    11,347

    *

    Quote Originally Posted by steve3871m View Post
    #1. Remove Goodboy equipment.
    #2. Discard in trash receptacle.
    #3. Install professional brand equipment.

    what equipment do you prefer?

    does this mean you wont fix anything unless it is your favorite equipment?



    .

  5. #5
    Join Date
    Dec 2006
    Location
    Middle Tennessee
    Posts
    11,347

    *

    Quote Originally Posted by youngtech View Post
    Working on a 2 year old GMS90703BXA, condensate will not drain while its running. Shut it off it'll drain. Nothing is plugged.
    for starters, i would at least make sure the trap had water in it!



    .

  6. #6
    Join Date
    Dec 2003
    Location
    Location!, Location!
    Posts
    929
    A qualified tech should check all the hoses, fittings, and trap. If that's you-register as pro.

  7. #7
    Join Date
    Jan 2007
    Location
    NE OHIO
    Posts
    778
    Quote Originally Posted by rimek View Post
    A qualified tech should check all the hoses, fittings, and trap. If that's you-register as pro.
    in process of doing just that

  8. #8
    Join Date
    Jan 2007
    Location
    NE OHIO
    Posts
    778
    Quote Originally Posted by Airmechanical View Post
    for starters, i would at least make sure the trap had water in it!



    .
    it does have water in it, first time i ever saw a trap like this. It is open at the top, you can look right in it

  9. #9
    Join Date
    Dec 2003
    Location
    Location!, Location!
    Posts
    929
    Yes it is-don't be scared- check all the other things mentioned.

  10. #10
    Join Date
    Nov 2001
    Location
    east kansas
    Posts
    8,038
    Check to make sure all the condensate lines are in their proper position. Have to get the book out for this one.

  11. #11

    Goodman

    You are lucky if that is the only problem you have with the Goodman. Don't worry you will get to change the fan relay soon.

  12. #12
    Join Date
    Nov 2006
    Location
    california
    Posts
    54
    make sure drain system is setup correctly
    trap set is correctly configure
    check for air leak

  13. #13
    Join Date
    May 2000
    Location
    Urbandale IA. USA
    Posts
    4,962
    Quote Originally Posted by youngtech View Post
    Working on a 2 year old GMS90703BXA, condensate will not drain while its running. Shut it off it'll drain. Nothing is plugged.
    Do you have pictures you could post?
    If any one shortened the plastic pipes that stick down into the trap, it will change the characteristics of the trap.
    The top of the trap MUST be lower than 2" below the hole in the side of the furnace for the drain to work properly.

    Does it drain with the top access pannel removed? If it does, you could have a combustion air supply problem.

    Measure the static pressure at the collection box cover drain with a mannometer to see what the inducer is doing.

    For MOST brands the inducer will pull 2" wc and therefore the trap must be lower than 2" below the lowest condensing tap....

    Ignore those who belittle Goodman, they are jellous that they cannot compete with price and generaly repair the ones that have been improperly installed in the first place...
    Last edited by cehs; 01-29-2007 at 09:23 AM.
    Those who dance, appear insane to those who do not hear the music.
    Those who believe, appear ignorant to those who do not know God.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event