Trane RTU Test Mode
Hello everyone,
Earlier today I was trying to get a Trane RTU to start in test mode. Simple enough, just jump LTB 1 and LTB 2 and sit back and wait. The only problem is that it just got stuck in step 1 (the blower or something--can't recall) for 10 or 15 minutes before I gave up. The compressors never energized. I tried the test in two different ways:
1) Turn power off, put jumpers on, turn power back on and wait for test mode to start
2) Turn power off, turn power back on, then put jumpers on and wait for test mode
Neither way seemed to knock any sense into the thing. I got it to work on two other Trane units earlier in the day, maybe I was just tired
Am I missing something?
-
03-20-2013, 08:38 PM #2
Professional Member
- Join Date
- Mar 2011
- Location
- North Carolina Piedmont Area
- Posts
- 293
Is this a Microtel control board
-
03-20-2013, 09:01 PM #3
Regular Guest
- Join Date
- Mar 2013
- Posts
- 36
-
03-20-2013, 09:06 PM #4
Professional Member
- Join Date
- Mar 2011
- Location
- North Carolina Piedmont Area
- Posts
- 293
There are two type of boards. Microtel or the new Reliatel board.
If you are trying to test from the LTB test 1 & 2, you will need to verify that the wire plug is connected to the board.
You really should be using a decade box for variable resistance testing.
What is the Model No. and Serial No.
-
03-20-2013, 09:48 PM #5
Regular Guest
- Join Date
- Mar 2013
- Posts
- 36
-
03-20-2013, 10:00 PM #6
Professional Member*
- Join Date
- Feb 2006
- Location
- Atlanta,GA.
- Posts
- 729
f its not reliatel it is not ltb1 & 2 it is test 1&2 two different sets of terminals on low voltage terminal board
-
03-20-2013, 10:10 PM #7
correct me if i am wrong but if i remember correctly, to use test mode without resistors, you need to jumper the terminals for one second and then remove jumper. to move to next test function jump T1 & T2 again for one second so on and so forth. hope this helps!
-
03-20-2013, 10:14 PM #8
Professional Member
- Join Date
- Mar 2011
- Location
- North Carolina Piedmont Area
- Posts
- 293
-
03-20-2013, 10:22 PM #9
Professional Member
- Join Date
- Mar 2011
- Location
- North Carolina Piedmont Area
- Posts
- 293
As the OP has stated he has ran this unit in test mode for 15 minutes and has clearly lost his position. In this case there is no other or better method than to use a decade box. But if he does not have one than he can simply purchase a resistor as stated in the troubleshooting manual and test the mode which is of concern.
Otherwise he will need to be certain that he has tapped the terminals and follow the sequence so that he will be in the correct mode. Even for a very experienced tech and when experiencing erratic behavior it is difficult to follow the modes......nothing beats a decade box.
-
03-20-2013, 10:41 PM #10The weak aren't destroyed by the strong.
The weak are destroyed by the under-estimated.
I know a famous song that ends in 'my nose'. The artist is dead. Know who?
-
03-20-2013, 10:48 PM #11
Yes I know that but the way the OP was written it sounded like he put the jumper between t1&t2 and left it in place. Maybe I read it wrong.
-
03-21-2013, 04:54 PM #12
New Guest
- Join Date
- Mar 2010
- Posts
- 4
-
03-21-2013, 05:30 PM #13
Regular Guest
- Join Date
- Jul 2008
- Location
- NEW JERSEY
- Posts
- 31
With jumper left in place unit will change steps every 30 seconds. For those without patience (like myself) take the jumper off for a five count then back on for five to get to the step you want. Will not go to a step with a safety open (limit/switch). Should also see the RTRM or UPC light flashing which indicates unit is in test mode.