    Carrier 38QRR with standard blower

    Quick question, I have to install a Carrier 38QRR compact heat pump next week. It is going to matched with a standard air handler, not the ductless one carrier sells. I was reading the manual and it shows installing the PISTON at the heat pump service valve. For what I read in the manual its only needed when using the ductless air handler. I just wanted to confirm that this is correct.

    Thanks
    Chris

  2. #2
    Join Date
    Jul 2007
    Location
    Virginia
    Posts
    5,593
    Quote Originally Posted by croft1972 View Post
    Quick question, I have to install a Carrier 38QRR compact heat pump next week. It is going to matched with a standard air handler, not the ductless one carrier sells. I was reading the manual and it shows installing the PISTON at the heat pump service valve. For what I read in the manual its only needed when using the ductless air handler. I just wanted to confirm that this is correct.
    When in heating mode, the refrigerant will need to be metered at the outdoor unit also.

    The install manual I have states a hard shutoff TXV is required at the indoor unit, and the Check AccuRater device (field replaceable piston), which is supplied with the unit, is to be installed at the outdoor unit service valve.

    As far as I know, there is no metering device internal to the 38QRR (outdoor unit) for use in heating.
    Instead of learning the tricks of the trade, learn the trade.

  3. #3
    Join Date
    Jul 2006
    Location
    NJ
    Posts
    239
    Thanks.