  1. #27

    HOW ABOUT THIS FO AN IDEA

    Quote Originally Posted by Moparmyway View Post
    Got the new Blue Vac to use today, as well as the new sensor for the YJ setup. Both were within50 microns of each other the entire way from atmospheric down to 150 microns !

    I love the Blue Vac's programmable alarm, I set mine so that after 15 minutes @ 250 microns or less, it starts chirping ...................... AWESOME !!!!!
    HERE'S AN IDEA:

    BluVac wireless compatibility with FP and Testo.

  2. #28
    Join Date
    May 2010
    Location
    Canada
    Posts
    686
    Hey Joey,

    Every now and then my Bluvac will act up a bit after I disconnect it from a vacuum. The other day it took around 20sec to read above 25000microns. I cleaned the sensor and threw it in the freezer but it still does this once in a while. I'm wondering if maybe it's the Nylog. The performance of the Bluvac is not affected at all ( I compared it to my other Bluvac) and the readings were within 10% of each other.

    Any suggestion?

  3. #29
    Join Date
    Sep 2005
    Location
    Atlanta GA area
    Posts
    20,251
    Quote Originally Posted by Moparmyway View Post
    If I cant clean it, and I have to purchase another sensor, I am gunna get a Blue Vac instead !!!!!!!!!
    If you decide you do not want that YJ... send me a PM... maybe we can cut a deal.
    GA-HVAC-Tech

    Galatians 2:20-21; Colossians 1: 21-22 & 26-27; 3:1-4; Romans Ch's 5-6-7-8

    2 Chronicles 7:14

    Quality work at a fair price with excellent customer service.

  4. #30
    Join Date
    May 2011
    Location
    New York
    Posts
    304
    Quote Originally Posted by ga-hvac-tech View Post
    If you decide you do not want that YJ... send me a PM... maybe we can cut a deal.
    Gunna keep them both ............ since I was able to source the vacuume sensor for under $60, the YJ is back in service, and I love the BV, so they are both keepers !
    Extended dehydration is the key

  5. #31
    Join Date
    Aug 2010
    Location
    Florida
    Posts
    203
    Quote Originally Posted by eddiegoodfellar View Post
    Every now and then my Bluvac will act up a bit after I disconnect it from a vacuum. The other day it took around 20sec to read above 25000microns.
    This is caused by residual refrigerant gas in the sensor port. Next time you see this happen, gently blow a little air into the port, and you'll see the gauge go to Hi-P immediately.

    This is not an effect specific to the BluVac. All micron gauges using thermal conductivity to measure vacuum will be affected similarly (and equally!). Since the BluVac responds so much faster than other gauges, the effect is more apparent.

  6. #32
    Join Date
    May 2010
    Location
    Canada
    Posts
    686
    Quote Originally Posted by joeyd View Post
    This is caused by residual refrigerant gas in the sensor port. Next time you see this happen, gently blow a little air into the port, and you'll see the gauge go to Hi-P immediately.

    This is not an effect specific to the BluVac. All micron gauges using thermal conductivity to measure vacuum will be affected similarly (and equally!). Since the BluVac responds so much faster than other gauges, the effect is more apparent.
    Thank you.

  7. #33
    Join Date
    May 2011
    Location
    New York
    Posts
    304
    Quote Originally Posted by joeyd View Post
    This is caused by residual refrigerant gas in the sensor port. Next time you see this happen, gently blow a little air into the port, and you'll see the gauge go to Hi-P immediately.

    This is not an effect specific to the BluVac. All micron gauges using thermal conductivity to measure vacuum will be affected similarly (and equally!). Since the BluVac responds so much faster than other gauges, the effect is more apparent.
    Hi Joeyd,
    I MUST admit, the more I use your Blue Vac, the more I like it !!!!
    I am learning to trust it as I do my YJ setup, and one of my vac pumps pulled down to 1.5 microns with 10 ' of 1/4" copper tubing attached.
    Great product @ a great price............ I can get 4 BV's for another YJ setup ............... am gunna order a few more BV's in the next few months !!!!
    Extended dehydration is the key

Page 3 of 3 FirstFirst 123

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event