    Mar 2013
    Dual 4 ton txv's on 7.5 ton coil- 1 icing, the other seems normal
    I have something i have not seen before. carrier 7.5 ton r-22 evap with 2 four ton txvs. One is icing at the manifold and the other is not. I replaced the icing valve and got same results. Anyone seen this before? Thanks. 5/8 liquid line splits into 2 1/2 inch lines, go into seperate txv and suction lines join at outlet of air handler to return to condenser in 1 1/8 line.
    Salisbury, Maryland
    Got any other data? OD temp, superheat, subcooling, pressures?
    East of big city prices.
    Maybe even equipment model #'s too. So we can get an idea of what you are working with.
    Mar 2013
    Sorry, Carrier 40rm012 air handler, 7.5 ton trane condenser, 85 oda 250 head/50 back 23 delta t on saturday, yesterday told it was 85oda, 30 back 210 head and 15 delta. Upper txv circuit icing. lower not.
    Nov 2009
    Central Virginia
    85 outdoor air and are you saying you had a 50psi suction pressure? Just wanna be sure Im reading that right.
    Sent from my SPH-D710 using Tapatalk 2
    ____________________________________________
    If you don't know what you are doing.... ASK!! There is no such thing as a "Stupid" question.... Maybe.
    Mar 2013
    yes, 50 suction and 250 at liquid service port.