Page 5 of 9 FirstFirst 123456789 LastLast
Results 53 to 65 of 106
Thread: r22 conversions
  1. #53
    Good - that will save me working out the performance numbers on my own.
    As soon as one of my A/C units needs anything I am going to build my next A/C unit to use R-134A.
    PHM
    Quote Originally Posted by icemeister View Post
    Copeland appears to be heading back to doing that with their new FFAP scroll condensing units which are compatible with R134A, R404A, R22 and R407C:
    Attachment 385461
    PHM
  2. #54
    Jul 2011
    Lehigh Valley, PA
    Quote Originally Posted by Trehak01 View Post
    What about MO99? Anyone have any insight of this being a better replacement? what are the pros and cons?
    I've converted four systems to R438. Two split systems where I installed new dry charged POE outdoor condensing units to concealed air handlers in attics. Followed best practices, added suction, liquid filters & changed all sch valves. pressured tested with n2 & pulled low vac. Charged to 6F-8F sub-cool. Units working good but it hasn't been super hot yet either. I'll be watching.
    The third was a larger 7.5 ton split with a Copeland scroll. This one has been good too. The 4th was on an old Carrier 10ton package unit with worn compressors. Not so good results but it's working. If I had newer compressors, I believe this unit would be working much better.
  3. #55
    Jun 2013
    Central Florida
    Our school district (31st largest out of 16,000 nationwide) began retrofitting a while back. After being warned in '98 about R22 going bye-bye the Facilities Dept kept spec'ing R22 equipment right up until 12 new schools and freshman academies opened in '10 with brand new R22 systems.
    Our purchasing department stopped approving R22 purchases when it hit $500, and forced the retrofitting issue. After careful research (and I mean a LOT), R-407C is our de-facto choice due to better capacity match, mass flow rate and lower discharge temps among other superiorities.
    Now, when I say 'our' you must realize that our immediate management lacks the resolution to make command decisions and upper management lacks the aptitude. Fortunately, nearly all of our mechanics support this and have no problem with performing a proper retrofit procedure.
    In all systems that can be drained or vacuumed of their MO, we are switching to R-407C and POE. Our results have been above our expectations; the systems exhibited exemplary cooling performance and energy consumption characteristics.
    All compressor changeouts have the MO replaced with POE before installation and are charged with R-407C; when possible, new and remanufactured compressors are purchased with POE oil charges.
    Unfortunately, a couple of people prefer what we refer to as a “drive-by” retrofit requiring mimimal labor on their part other than getting out of the truck and attaching their gauges.
    In a couple of these “drive-bys”, new compressors were installed with the MO and R-422D; the recommended addition of 20% POE oil was not followed. Honeywell and Johnstone are pushing this. (Can't wait to see how well the capacity loss is going to go over with the teachers when schools starts this August with 110+ degree heat index).
    We have found that in our MO units that can not be easily relieved of the MO charge, MO oil return with R-407C is successfully enhanced with the addition of Supco 88 to thin the MO, in place of the hydrocarbon content in 438A, 422D, etc.
    DuPont has acknowledged that the basic reason for the hydrocarbon content in these blends is to thin the MO in an effort to provide a bit of oil return; the more hydrocarbon in the blend, the better thinning of the MO.
    Supco 88 is 98%-99% hydrocarbons.
    With 'drop-in' refrigerants, ALWAYS read the fine print at the bottom that essentially says “Good luck on that workin for ya!”
  4. #56
    A few weeks ago I spoke with someone who should know and he said their testing showed that as little as 10% POE / 90% MO provided acceptable oil return.
    And also: some closed-system makers have been successfully running 407 over MO (zero POE content) without issue. PTAC's and the like.
    I have to do some 407C conversions soon so I will have a stock of 407C. So I have been thinking about pulling the R-22 out of the 30 year old Coleman 13 SEER for my 1st floor A/C system and installing 407C without any other changes. Out of the present evap there is a 13" riser to a reverse trap and then the suction line is dead level to the condensing unit. How much of an oil return issue can there Be? <g>
    What is the logic behind the +90% POE 'requirement' ?
    PHM
    Doing the oil changes ahead only makes sense because you know you'll have to do it eventually...unless the store is closing or planning a major remodel. The old standard for POE concentration is still 95%, but that was established way back in the early 1990s when the manufacturers really didn't have a good handle on how much mineral oil could be tolerated in a system. RobY was involved in this at the time and has commented on this numerous times, adding that much higher MO concentrations will work well with HFC refrigerants and that they're shooting for a goal of 50%, so only a single oil change would be needed.
    It's been widely discussed that the leaking seal issue is primarily due to their reaction to the presence of R22 (or any blend containing R22), causing them to swell. If the R22 is removed, they'll shrink and start to leak. I think changing seals before changing the gas might be taking a risk, but all I know is they will shrink quickly. I really don't have an idea of how long it takes them to swell up.
    So are we mainly talking about shraders and O-rings, or are other types of seals require replacing? IOW, On a typical market refrigerant retrofit, what seals are the main culprits?
    PHM
  5. #57
    Mar 2013
    swan valley idaho
    i was at a coss class a couple months ago. had a very smart older tech teaching it. he said while copeland wont "officially" say or recommend it, that yeah- close coupled systems like reach ins etc.... will work with no oil change at all, package ac units etc.... the OFFICIAL copeland recommendation is change to p.o.e. but he said he knows of lots of smaller close coupled systems running great without oil change.....
  6. #58
    Quote Originally Posted by kklobas View Post
    No different than when we ran 401a and other R-12 retrofits over mineral oil in small, unitary equipment...
  7. #59
    Mar 2013
    swan valley idaho
    the funny thing is i am still today running into alot of old systems in resteraunts here using 401,409,414 in the same building. i think i am going to try hot shot 2 for all this old r12 stuff left . i do mainly resteraunts, and believe it or not, most here in Idaho still have something that was originally r12. Ever tried hot shot 2?
  8. #60
    I just bought my first Hot Shot 2 cylinder. Years ago I switched from 409 to 414 (Hot Shot One) and found it worked well in everything so I kept using it. R-409 ran head pressure higher than I was ever happy with. R401 is pushing $600. per 30 - so I'm sure not using that.
    PHM
    PHM
  9. #61
    EMETH - please tell me more
    On what kinds of systems have you successfully used R-407C, running over mineral oil, by using the Supco 88 additive?
    Size? Configurations? Applications?
    PHM
    Quote Originally Posted by EMETH View Post
    Our school district (31st largest out of 16,000 nationwide) began retrofitting a while back. . . . After careful research (and I mean a LOT), R-407C is our de-facto choice due to better capacity match, mass flow rate and lower discharge temps among other superiorities . . . We have found that in our MO units that can not be easily relieved of the MO charge, MO oil return with R-407C is successfully enhanced with the addition of Supco 88 to thin the MO, in place of the hydrocarbon content in 438A, 422D, etc . . . DuPont has acknowledged that the basic reason for the hydrocarbon content in these blends is to thin the MO in an effort to provide a bit of oil return; the more hydrocarbon in the blend, the better thinning of the MO.
    Supco 88 is 98%-99% hydrocarbons . . .
    PHM
  10. #62
    Jun 2013
    Central Florida
    The largest so far is a 10-ton Trane split on a locker room; most everything larger is either semi-hermetic which we can vacuum out the MO and install POE, or scrolls with removable oil sight glasses.
    A lot of Bard and Marvaire wall hungs up to 5 tons and various other package units and PTACs. Longest lineset so far is a 5 ton with about 75 feet underground.
    PHM
  11. #63
    So you have a 10 ton Trane split (the locker room) running R407C, mineral oil, and Supco 88 ? Yes?
    And you have a 5 ton split, with a 75' underground lineset, running R407C, mineral oil, and Supco 88 ? Yes?
    PHM
    PHM
  12. #64
    Jun 2013
    Central Florida
    Yes to both; the 10 ton is a heat pump with the big red compressor that is also the accumulator. I think it's called a 'Climatuff'?
    I believe that's about the largest circuit we're going to find that doesn't have any way to remove the MO with removing the compressor.
  13. #65
    Jun 2013
    Central Florida
    Sorry, I meant 'withOUT' removing the compressor.