    Smardt Chiller Repair - Turbocor

    This was my first repair on a turbocor compressor. The IGV on compressor #1 stop responding.......couple months later compressor #2 IGV stop responding and got stuck in a fixed position just like #1 compressor. We talked to DTC they said there was a problem with some of the IGVs installed on some of the ealier compressors. Just finished up the repair today...... compressors came online and loaded up correctly.

    Name:  photo 2 (2).jpg
Views: 4929
Size:  39.9 KBName:  photo 1 (3).jpg
Views: 5303
Size:  41.7 KBName:  photo 2 (3).jpg
Views: 4446
Size:  43.9 KBName:  photo 3 (2).jpg
Views: 4203
Size:  39.6 KBName:  photo 4 (2).jpg
Views: 4930
Size:  43.8 KB
    RTFM!!!

  2. #2
    Join Date
    Dec 2011
    Location
    Australia
    Posts
    18
    Post Likes
    Looks good. What was the problem with the IGV? What year was the compressor built?

  3. #3
    Join Date
    Oct 2005
    Location
    USA
    Posts
    615
    Post Likes
    Thread Starter
    The IGV was stuck at 20% it would not open or close.

    I just realized I posted in the wall of shame Can someone move it to the commercial forum.
    RTFM!!!

  4. #4
    Join Date
    Jul 2006
    Location
    Anytown USA
    Posts
    2,257
    Post Likes
    Thanks for sharing the pictures

  5. #5
    Join Date
    Jan 2011
    Posts
    1,581
    Post Likes
    Quote Originally Posted by manny238 View Post
    The IGV was stuck at 20% it would not open or close.

    I just realized I posted in the wall of shame Can someone move it to the commercial forum.
    I was wondering why this was in the HOS! Ping one of the moderators, they can move it for you.

  6. #6
    Join Date
    Dec 2011
    Location
    Australia
    Posts
    18
    Post Likes
    Did the ball bearing in the peep window indicate that it was stuck at 20% Or did it move the full 0-100 range? Did the IGV test ok?

  7. #7
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,690
    Post Likes
    Moved to Tech to Tech Chat Commercial



  8. #8
    Join Date
    Oct 2005
    Location
    USA
    Posts
    615
    Post Likes
    Thread Starter
    Nope the ball bearing would not move...... also ran numerous test on the IGV it would not respond at all.
    RTFM!!!

  9. #9
    Join Date
    Oct 2014
    Posts
    3
    Post Likes
    hi, i have a problem with a turbocor, the control board dont have power, i need a service manual or some kind of help.

  10. #10
    Join Date
    May 2015
    Posts
    1
    Post Likes
    Quote Originally Posted by jpsmith1cm View Post
    Moved to Tech to Tech Chat Commercial
    Hi, we installed two TT-300 and have some problems.

  11. #11
    Join Date
    Jul 2011
    Location
    Aurora
    Posts
    242
    Post Likes
    Quote Originally Posted by manny238 View Post
    The IGV was stuck at 20% it would not open or close.

    I just realized I posted in the wall of shame Can someone move it to the commercial forum.
    what happen to the operation before repaired? did it not maintaining set point or else?
    we have thermal care chiller that using 2 turbocore compressor. so far is operate smoothly.

  12. #12
    Join Date
    Oct 2005
    Location
    USA
    Posts
    615
    Post Likes
    Thread Starter
    Quote Originally Posted by cfe View Post
    what happen to the operation before repaired? did it not maintaining set point or else?
    we have thermal care chiller that using 2 turbocore compressor. so far is operate smoothly.
    Could not maintain set point.


    Sent from my iPhone using Tapatalk
    RTFM!!!

  13. #13
    Join Date
    Jun 2015
    Posts
    8
    Post Likes
    if IGV works correctly, it will open 110% in maximum position

  14. #14
    Join Date
    Jul 2011
    Location
    Aurora
    Posts
    242
    Post Likes
    Quote Originally Posted by manny238 View Post
    Nope the ball bearing would not move...... also ran numerous test on the IGV it would not respond at all.
    how do you test the IGV operation? is it thru the I/0 connector and danfoss sofware on your computer ?
    i have a turbocor compressor # 2 that IGV only go up to 12 % . the ball bearing not even move stay closed.
    after numerous time its tripped. no refrigeration effect at all.

    did not see any option on chiller control panel. this is Arctic cool chiller.

  15. #15
    Join Date
    Jun 2008
    Location
    Windsor, Ont.
    Posts
    894
    Post Likes
    Quote Originally Posted by cfe View Post
    how do you test the IGV operation? is it thru the I/0 connector and danfoss sofware on your computer ?
    i have a turbocor compressor # 2 that IGV only go up to 12 % . the ball bearing not even move stay closed.
    after numerous time its tripped. no refrigeration effect at all.

    did not see any option on chiller control panel. this is Arctic cool chiller.
    You test the IGV operation with Turbocor 3G software and a connection through the interface board..

  16. #16
    Join Date
    Apr 2009
    Location
    San Diego, CA
    Posts
    42
    Post Likes
    I had the same thing happen in January. Compressor #2 started then shut down after about 15 min. Bad drive motor.

  17. #17
    Join Date
    Jan 2008
    Location
    Phoenix Arizona
    Posts
    1,663
    Post Likes
    the manufacturer of the chiller should be able to provide the Turbocor service manual...You might be able to find the new one online, I couldn't but didn't look very hard...There is a section in the back on how to test and verify almost everything in the compressor...You have to put it in manual mode and set the IGV steps. I believe around 12000 is full open 6000 is around 50 and should be the starting percentage...

    Your starting % and max steps could be off and causing problems...I check a known good compressor's values when I run into these problems...
    "If history repeats itself I am so getting a dinosaur"

  18. #18
    Join Date
    Jun 2015
    Location
    Toronto
    Posts
    1
    Post Likes
    You can put the compressor in manual control mode and open the IGV to 110% all through the SMT software

  19. #19
    Join Date
    Oct 2005
    Location
    USA
    Posts
    615
    Post Likes
    Thread Starter

    Smardt Chiller Repair - Turbocor

    Smardt had a problem on there first generation chillers where the set screw was coming loose. I know they sent me something about it, id have to check when I get home. The new IGV comes with a new redesigned suction cover. Still fits in the same as the old one.

    You can try to contact Smardt but I'm not sure how helpful they will be.


    Sent from my iPhone using Tapatalk
    RTFM!!!

  20. #20
    Join Date
    Dec 2012
    Location
    Lowell,MA
    Posts
    69
    Post Likes
    turbocor.com

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •