    Smardt Chiller Repair - Turbocor

    This was my first repair on a turbocor compressor. The IGV on compressor #1 stop responding.......couple months later compressor #2 IGV stop responding and got stuck in a fixed position just like #1 compressor. We talked to DTC they said there was a problem with some of the IGVs installed on some of the ealier compressors. Just finished up the repair today...... compressors came online and loaded up correctly.

    Name:  photo 2 (2).jpg
Views: 1421
Size:  39.9 KBName:  photo 1 (3).jpg
Views: 1443
Size:  41.7 KBName:  photo 2 (3).jpg
Views: 1241
Size:  43.9 KBName:  photo 3 (2).jpg
Views: 1238
Size:  39.6 KBName:  photo 4 (2).jpg
Views: 1270
Size:  43.8 KB
    RTFM!!!

  2. #2
    Join Date
    Dec 2011
    Location
    Australia
    Posts
    18
    Post Likes
    Looks good. What was the problem with the IGV? What year was the compressor built?

  3. #3
    Join Date
    Oct 2005
    Location
    USA
    Posts
    443
    Post Likes
    The IGV was stuck at 20% it would not open or close.

    I just realized I posted in the wall of shame Can someone move it to the commercial forum.
    RTFM!!!

  4. #4
    Join Date
    Jul 2006
    Location
    Anytown USA
    Posts
    2,072
    Post Likes
    Thanks for sharing the pictures

  5. #5
    Join Date
    Jan 2011
    Posts
    1,400
    Post Likes
    Quote Originally Posted by manny238 View Post
    The IGV was stuck at 20% it would not open or close.

    I just realized I posted in the wall of shame Can someone move it to the commercial forum.
    I was wondering why this was in the HOS! Ping one of the moderators, they can move it for you.

  6. #6
    Join Date
    Dec 2011
    Location
    Australia
    Posts
    18
    Post Likes
    Did the ball bearing in the peep window indicate that it was stuck at 20% Or did it move the full 0-100 range? Did the IGV test ok?

  7. #7
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,378
    Post Likes

  8. #8
    Join Date
    Oct 2005
    Location
    USA
    Posts
    443
    Post Likes
    Nope the ball bearing would not move...... also ran numerous test on the IGV it would not respond at all.
    RTFM!!!

  9. #9
    Join Date
    Oct 2014
    Posts
    3
    Post Likes
    hi, i have a problem with a turbocor, the control board dont have power, i need a service manual or some kind of help.

  10. #10
    Join Date
    May 2015
    Posts
    1
    Post Likes
    Quote Originally Posted by jpsmith1cm View Post
    Moved to Tech to Tech Chat Commercial
    Hi, we installed two TT-300 and have some problems.

  11. #11
    Join Date
    Jul 2011
    Location
    SLO/central coast
    Posts
    188
    Post Likes
    Quote Originally Posted by manny238 View Post
    The IGV was stuck at 20% it would not open or close.

    I just realized I posted in the wall of shame Can someone move it to the commercial forum.
    what happen to the operation before repaired? did it not maintaining set point or else?
    we have thermal care chiller that using 2 turbocore compressor. so far is operate smoothly.

  12. #12
    Join Date
    Oct 2005
    Location
    USA
    Posts
    443
    Post Likes
    Quote Originally Posted by cfe View Post
    what happen to the operation before repaired? did it not maintaining set point or else?
    we have thermal care chiller that using 2 turbocore compressor. so far is operate smoothly.
    Could not maintain set point.


    Sent from my iPhone using Tapatalk
    RTFM!!!

  13. #13
    Join Date
    Jun 2015
    Posts
    8
    Post Likes
    if IGV works correctly, it will open 110% in maximum position