Results 1 to 13 of 20
    Oct 2005
    Smardt Chiller Repair - Turbocor
    This was my first repair on a turbocor compressor. The IGV on compressor #1 stop responding.......couple months later compressor #2 IGV stop responding and got stuck in a fixed position just like #1 compressor. We talked to DTC they said there was a problem with some of the IGVs installed on some of the ealier compressors. Just finished up the repair today...... compressors came online and loaded up correctly.
    Name:  photo 2 (2).jpg
Size:  39.9 KBName:  photo 1 (3).jpg
Size:  41.7 KBName:  photo 2 (3).jpg
Size:  43.9 KBName:  photo 3 (2).jpg
Size:  39.6 KBName:  photo 4 (2).jpg
    RTFM!!!
    Dec 2011
    Australia
    Looks good. What was the problem with the IGV? What year was the compressor built?
    Oct 2005
    The IGV was stuck at 20% it would not open or close.
    I just realized I posted in the wall of shame Can someone move it to the commercial forum.
    RTFM!!!
    Anytown USA
    Thanks for sharing the pictures
    Jan 2011
    Quote Originally Posted by manny238 View Post
    I was wondering why this was in the HOS! Ping one of the moderators, they can move it for you.
    Dec 2011
    Australia
    Did the ball bearing in the peep window indicate that it was stuck at 20% Or did it move the full 0-100 range? Did the IGV test ok?
    Oct 2005
    Nope the ball bearing would not move...... also ran numerous test on the IGV it would not respond at all.
    RTFM!!!
    Oct 2014
    hi, i have a problem with a turbocor, the control board dont have power, i need a service manual or some kind of help.
    May 2015
    Moved to Tech to Tech Chat Commercial
    Hi, we installed two TT-300 and have some problems.
    Jul 2011
    SLO/central coast
    what happen to the operation before repaired? did it not maintaining set point or else?
    we have thermal care chiller that using 2 turbocore compressor. so far is operate smoothly.
    Oct 2005
    Quote Originally Posted by cfe View Post
    Could not maintain set point.
    RTFM!!!
    Jun 2015
    if IGV works correctly, it will open 110% in maximum position