    Smardt Chiller Repair - Turbocor

    This was my first repair on a turbocor compressor. The IGV on compressor #1 stop responding.......couple months later compressor #2 IGV stop responding and got stuck in a fixed position just like #1 compressor. We talked to DTC they said there was a problem with some of the IGVs installed on some of the ealier compressors. Just finished up the repair today...... compressors came online and loaded up correctly.

    Name:  photo 2 (2).jpg
Views: 1365
Size:  39.9 KBName:  photo 1 (3).jpg
Views: 1384
Size:  41.7 KBName:  photo 2 (3).jpg
Views: 1200
Size:  43.9 KBName:  photo 3 (2).jpg
Views: 1194
Size:  39.6 KBName:  photo 4 (2).jpg
Views: 1220
Size:  43.8 KB
    RTFM!!!

  2. #2
    Join Date
    Dec 2011
    Location
    Australia
    Posts
    18
    Post Likes
    Looks good. What was the problem with the IGV? What year was the compressor built?

  3. #3
    Join Date
    Oct 2005
    Location
    USA
    Posts
    433
    Post Likes
    The IGV was stuck at 20% it would not open or close.

    I just realized I posted in the wall of shame Can someone move it to the commercial forum.
    RTFM!!!

  4. #4
    Join Date
    Jan 2011
    Posts
    1,374
    Post Likes
    Quote Originally Posted by manny238 View Post
    The IGV was stuck at 20% it would not open or close.

    I just realized I posted in the wall of shame Can someone move it to the commercial forum.
    I was wondering why this was in the HOS! Ping one of the moderators, they can move it for you.

  5. #5
    Join Date
    Jul 2011
    Location
    SLO/central coast
    Posts
    164
    Post Likes
    Quote Originally Posted by manny238 View Post
    The IGV was stuck at 20% it would not open or close.

    I just realized I posted in the wall of shame Can someone move it to the commercial forum.
    what happen to the operation before repaired? did it not maintaining set point or else?
    we have thermal care chiller that using 2 turbocore compressor. so far is operate smoothly.

  6. #6
    Join Date
    Oct 2005
    Location
    USA
    Posts
    433
    Post Likes
    Quote Originally Posted by cfe View Post
    what happen to the operation before repaired? did it not maintaining set point or else?
    we have thermal care chiller that using 2 turbocore compressor. so far is operate smoothly.
    Could not maintain set point.


    Sent from my iPhone using Tapatalk
    RTFM!!!

  7. #7
    Join Date
    Jun 2015
    Posts
    8
    Post Likes
    if IGV works correctly, it will open 110% in maximum position

  8. #8
    Join Date
    Apr 2009
    Location
    San Diego, CA
    Posts
    42
    Post Likes
    I had the same thing happen in January. Compressor #2 started then shut down after about 15 min. Bad drive motor.

  9. #9
    Join Date
    Jul 2006
    Location
    Anytown USA
    Posts
    2,070
    Post Likes
    Thanks for sharing the pictures

  10. #10
    Join Date
    Dec 2011
    Location
    Australia
    Posts
    18
    Post Likes
    Did the ball bearing in the peep window indicate that it was stuck at 20% Or did it move the full 0-100 range? Did the IGV test ok?

  11. #11
    Join Date
    Oct 2005
    Location
    USA
    Posts
    433
    Post Likes
    Nope the ball bearing would not move...... also ran numerous test on the IGV it would not respond at all.
    RTFM!!!

  12. #12
    Join Date
    Jul 2011
    Location
    SLO/central coast
    Posts
    164
    Post Likes
    Quote Originally Posted by manny238 View Post
    Nope the ball bearing would not move...... also ran numerous test on the IGV it would not respond at all.
    how do you test the IGV operation? is it thru the I/0 connector and danfoss sofware on your computer ?
    i have a turbocor compressor # 2 that IGV only go up to 12 % . the ball bearing not even move stay closed.
    after numerous time its tripped. no refrigeration effect at all.

    did not see any option on chiller control panel. this is Arctic cool chiller.

  13. #13
    Join Date
    Jun 2008
    Location
    Windsor, Ont.
    Posts
    572
    Post Likes
    Quote Originally Posted by cfe View Post
    how do you test the IGV operation? is it thru the I/0 connector and danfoss sofware on your computer ?
    i have a turbocor compressor # 2 that IGV only go up to 12 % . the ball bearing not even move stay closed.
    after numerous time its tripped. no refrigeration effect at all.

    did not see any option on chiller control panel. this is Arctic cool chiller.
    You test the IGV operation with Turbocor 3G software and a connection through the interface board..