    Have large residential apartment complex, units have fixed orifice, will be charging by superheat but cannot gain access to suction line leaving evaporators. What should the superheat reading be at compressor suction line?
    Tallahassee, FL
    That's goona vary too much depening on where each lineset runs and how long.
    May 2011
    Ripley, WV
    I always check my superheat at the outdoor unit near the suction service valve and I just use a standard superheat calculator to make that determination. I wouldn't think there would be enough difference between checking at the Evaporator outlet and the outside unit to matter unless you have a long run of lineset that is in direct sunlight.
    SB is it better in your opinion to check SH at the indoor coil?
    Last edited by Rob_in_WV; 03-19-2013 at 08:04 PM. Reason: added a question to end.
    Tallahassee, FL
    Well I do always check it at evap if I'm going to add any. Especially if its a txv.
    Buried linesets/ long lines in attic can pick up 10deg pretty easily in my experience.
    Phoenix, AZ
    I would check the manufacture charging specs. For superheat most of the time they want you to take suction line temp at compressor or at the suction line entering at condensing unit.
    St Paul, minnesota
    Quote Originally Posted by SBKold View Post
    What is this refrigeration 101?
    He said he had units with a fixed orifice I:E a piston. In that case you take superheat 4-6" before the suction line service valve on the condensing unit and if it's a TXV then you don't take superheat readings, you take subcool readings.
    buried and long linesets should be TXV only. again subcool readings, not superheat
    Dec 2012
    columbus, OH
    If they will not let you access the evaporator I would just do my best and not worry about it.
    May 2011
    Ripley, WV
    Quote Originally Posted by superfittertech View Post
    I always verify both with a TXV so that I know the valve is metering correctly.
    St Paul, minnesota
    Quote Originally Posted by Rob_in_WV View Post
    Either way you still take your readings @ the condensing unit
    Mn the state where absolutey nothing is allowed
    Quote Originally Posted by atlantis View Post
    need to know the outside DB and evap inlet WB to get tareget SH, plus ensure proper airflow to know if your measured SH is even correct.
    we have a winner!
    yes, but if you cannot get inside whats the point? ( see above)
    my boss thinks its possible to repeal the laws of physics
    Jun 2009
    South Carolina
    Disagree with ya there
    some places with poor armorflex and/or 50' lineset in a attic that is 130 F
    i do check on the outside and if it looks normal then i may not check coming out of the IDC. But if the SH seems high i prefer to go check it coming out of the coil so i can see what is going on with the system. JMO
    May 2011
    Ripley, WV
    *We are the Champions starts Playing loudly in the background.*
    CH4MAN what did I win?
    Quote Originally Posted by klee7013 View Post
    So you have schrader fittings at the IDC of these units. Or you just guess what the pressure is at the IDC.