  1. #66
    Join Date
    Mar 2013
    Posts
    24
    heartman, I didn't see your post when responding above. What you're saying makes sense. At this point I think I need to bite the bullet and have another audit company out. I was trying to avoid it since it's ~$500 for another company. She did have an IR camera during the test. I saw all the blue areas around the fireplace and kitchen bump outs and a lot of the exterior outlets. I also saw the blue creeping down the outside walls on the second floor. That's when she said my top plates were leaky. I think you're right that a smoke machine would help.

    It's strange because even with the duct system being so tight, I still have those drafts. The duct blasting tech really wasn't sure why. He thought it was convection, my returns are only R-6.

  2. #67
    Join Date
    Aug 2004
    Location
    S.E. Pa
    Posts
    6,231
    They should not have been running the test with an atmospherically vented furnace running. That could put you at risk of CO exposure and they should know better.

    They should have taken a baseline for the Stack Effect With Respect To (WRT) outdoors. With 3 stories, yes, you can have significant stack effect alone in such a voluminous house. As the warm air rises, it creates a suction below. If there are upper level leaks or exfiltration, this gets exacerbated. You could install a makeup air (MUA) system that basically controls where the leaks are below the NPP and how much but it will add to the CFM 50. For the furnace to kick out on pressure switch, there has to be significant depressurization. Did they conduct a Worst Case Depressurization Test and if so, what was the result? If your furnace is a two pipe high efficiency unit the test should have no effect. Should... The tech should have been monitoring for backdrafting with a CO analyzer btw even with pilots at standby or the furnace off as in turned off at the disconnect. The furnace is powered 'on' only when you want to specifically test the effects of the air handler, such as during a Worst Case test. The little bit of makeup air used by such a furnace rarely contributes significantly to depressurization but interzonal competition from unsealed or imbalanced ducts can be huge. You can have a tight shell but a zonal conflict btw one part of the house with another that can cause infiltration. For instance, returns are fixed orifices while supply registers can be closed. If you close off a few supplies, such as in a seldom used room, you can create an imbalance in the system. More air gets sucked out at the return but not enough supply air enters the space to balance it resulting in a localized or microclimate depressurization.

    When there is a radon system installed, it should be tested for depressurization. First turn off the radon fan and get your baseline Stack Effect WRT outdoors. Then turn on the fan and repeat. The difference is how much, if any depressurization is being caused by an improperly sealed radon sub-slab suction system. Those WRT's need to be recorded on opposite sides of the house, esp. if there is more than a 5mph wind blowing--upwind and downwind sides. Air the infiltration points located at what is commonly the downwind or leeward side of the home?

  3. #68
    Join Date
    Oct 2006
    Location
    So. NH
    Posts
    748
    The N factor is a number from a chart based on your region, # of stories and shielding and is used in a formula to convert to ACHn [natural air changes] from CFM50. It's just another way to look at the data in the real world as opposed to CFM50 [the force of 20 mph wind on the house]. It's not absolute but just another tool. As far as the test it is an odd feeling the first time you experience it, you are indeed in negative pressure, -50 pa and is normal. It doesn't matter if the house is leaking allot or not, it's still -50 and that furnace should have been shut off.

    The lack of house wrap may be a factor here, it could be leading to leakage withing the walls that is fairly well sealed to the inside. it deserves more thought.

    As far as another test I would have the first one back since since you have had no follow up and they included it. You don't really have anything to lose and it may have been a simple mistake like having the gauge set for the wrong ring and they missed it. Since they then thought it was real tight they cut off the search for leaks too soon. Just a guess but nothing to lose by giving them another chance.

  4. #69
    Join Date
    Mar 2013
    Posts
    24
    The furnace wasn't on when the test was conducted, she set the thermostat to off before the test started. But as soon as the blower was powered on we noticed the display went off on the thermostat. It's a power stealing thermostat, so the control board in the Trane furnace shutdown the power to the thermostat. The display only came back once I power cycled the furnace breaker after the blower door test. The furnace has a single metal draft assisted flue going up and out the attic.

    As far as I know they didn't conduct any worst case depressurization tests. She didn't run any tests with the basement or attic unit running.

    At the time I had the audit, I didn't have the active radon fan. It was installed a few months after. So I'll ask them to include the radon fan in the new tests.

  5. #70
    Join Date
    Mar 2013
    Posts
    24
    stvc, makes sense. I'm going to request the test out now. I'll post back the results after the test. I'll also ask if they have a smoke machine. Even if I have to pay extra I think it's worth it!

    Thanks!

  6. #71
    Join Date
    May 2004
    Location
    south louisiana
    Posts
    3,235
    this may be obvious...but sometimes obvious things get over looked.
    as the first test was prior to mechanical ventilation install, make sure
    that the mechanical ventilation is sealed off prior to testing or it
    will skew all the readings.

    test in ..test out (or pre & final testing) was this included
    in the cost? if so, then use thie final test out for the next round.

    "The lack of house wrap may be a factor here, it could be leading to leakage withing the walls
    that is fairly well sealed to the inside. it deserves more thought."
    I agree. since reading that there was no wrap behind brick/vinyl this has been on my mind.
    how in the heck did it pass code?
    bricks don't stop moisture, and vinly is a very leaky product...why have there been no
    moisture intursion issues? maybe some of the blue in the thermal scan of the walls
    was moisture??
    I dunno. still thinking abou this.

    as I have no exprience in basements or radon vents...I'll leave that to those
    of you who do have experience with these areas.
    water table is too high here in La for basements, and radon is very low here.

    and hearthman...back on the first page traverty talks about a mechanical
    ventilation system installed after blower door test by another company.
    just fyi.
    The cure of the part should not be attempted without the cure of the whole. ~Plato

  7. #72
    Join Date
    Aug 2004
    Location
    S.E. Pa
    Posts
    6,231
    We've covered so much ground here, I'm kinda' losing track. I see where it appears they installed an HRV after the test, correct? Calling it "mechanical ventilation" was confusing me. An HRV properly set up normally does not affect the ACH and is not used for MUA--it is balanced in and out.

    One question for the OP: where does the NPP tend to lurk? Is it down about belt level on the first floor or higher up?

    Brick veneer makes for a pretty tight envelope in some cases but can leak like a sieve depending upon how the drainage plane is managed at the top. If they used #15 felt or even grade 'D' building paper behind the brick veneer, that is not an air barrier so like ER La said, the ext. sheathing could be the source of the leakage.

    Glad you clarified about running the furnace during the test. They should have been clear about that. My recommendation is to place a low level CO monitor in the CAZ during the test to protect everyone in the building. An off the shelf UL listed CO alarm is junk and can get you sick or worse. Not always practical to keep running back to the CAZ with a combustion analyzer during the test, esp. with 3 floors.

    Vinyl siding is designed to breathe so it can dry to the exterior just like a rain coat. Brick veneer absorbs water then either dries to the outside or water is driven by vapor diffusion towards the dry interior where the drainage plane 'catches' it so it can escape at the weep holes providing no one plugged them up. A lot of masons are using plastic vents in head joints to allow venting while allaying anxieties over the possibility of bugs entering through the weep holes. An IR camera can be very useful in locating occult water penetration but you need about a 10*F temperature gradient to really see because it works off temp. differences to adjacent surfaces. This means IR thermography sometimes has to be scheduled at extreme times in the day to get enough delta T. Note that IR thermography is not an X-ray of the building though many think it is and some tout it that way. It shows surface temps. where its up to the operator to put those temps. into perspective such as missing insulation vs. moisture. A quality pin-type moisture meter with training are advised along with training & certification for the thermography.

  8. #73
    Join Date
    Dec 2002
    Location
    in a house, Appomattox, Va.
    Posts
    3,323
    I had another though or two.

    the chase/clearance for the flue pipe up out roof could be air flow route.

    the floor joists at each level could have openings to the exterior of home (band joists run around perimeter and floor joists butt into them). its likely plywood joints hit right at thsoe locations as well, giving lined up gaps for air intrusion. I'm assuming there is plywood on 100% of exterior as sheathing

    bathtub plumbing openings in floors, the stud cavities around the tub, an if a tub unit w/ integral top or has dropped ceiling over tub, plenty pathways there from floor to floor or into attic if on top floor.

    pvc radon riser, other plumbing, duct risers and the gaps around where penetrate floors

    voids inside walls where framed out for soffets, angled walls, etc.

    all these could be interconnected paths for airflow inside the walls where you can't see all them.

    Had one customer, return was in closet floor pulling through louver in door. the tub access door was gone, had been pulling air from attic through drop ceiling above tub, into wall studs and down through space under tub into return ductwork. sealed it up and his tub doesn't get cold in winter, hot in summer.

    you might try looking for "builders guide" book for your climate, Joseph Lstibureck
    Col 3:23


    questions asked, answers received, ignorance abated

  9. #74
    Join Date
    Dec 2002
    Location
    in a house, Appomattox, Va.
    Posts
    3,323
    seen plenty of cases, where insulation was stapled up, but there were voids in walls under the insulation, sometimes it falls down and you can see inside walls and feel the warm air leaking up
    Col 3:23


    questions asked, answers received, ignorance abated

  10. #75
    Join Date
    Oct 2006
    Location
    So. NH
    Posts
    748
    There certainly are many hidden places for leakage.

    Taverty - when the next blower door does get done make sure you have plenty of time to search around with it running. I'll see if I kind find a good list of places to look and post it.

    Still curious as heck to see if this one turns out different.

  11. #76
    Join Date
    Jul 2007
    Location
    Delaware
    Posts
    3,824
    Are they phony windows in the attic? Are they sealed?
    If you removed all the insulation in the attic you would find the hole in the top floor ceiling. It may be under that platform.

    If you are sucking massive amounts of air (negative pressure) into the return, bringing all that air into the attic, condition it, and then you spit it back into the house. But.....if you have supply air duct leaks into the attic, and not all that air makes it back into the dwelling, you create the exact problem you have.

    Yes. You should remove ALL the insulation on every duct in the attic, seal all connections and reinsulate.
    Last edited by energy star; 03-30-2013 at 08:55 PM.

  12. #77
    Join Date
    May 2004
    Location
    south louisiana
    Posts
    3,235
    stvc wrote:
    The lack of house wrap may be a factor here, it could be leading to leakage withing the walls that is fairly well sealed to the inside. it deserves more thought.

    we have covered a lot of ground in this thread.
    but for a minute lets go back to the stack effect, air in...air out...where this all started.

    I've been thinking about small cracks that have a large effect & where air
    gets in and gets out. no great big smoking gun so far...maybe there isn't one.

    so what about a smaller sized opening...that just keeps going on & on through out
    the house?
    just imagine that behind the ceiling moldings & behind the floor moldings that
    you have a gap that is covered..much like the gaps hidden by bath vent fan covers
    & supply grills.
    only this gap is 1/8" to 1/2". not so big is it? but look at the linear feet of each wall.
    this adds up big.

    if this gap is behind the ceiling molding, extreme attic temps are on one side.
    if the gap is behind the floor moldings, temps are less extreme, but still
    problematic. air in...air out.

    while this usually is an older house issue,
    but in new construction, not all sheetrock finishers seal
    this gap.
    this is why I tell homeowners to tell finishers that they are not
    installing ceiling moldings..this way this gap is taped & floated.

    finish carpenters install moldings, painter may or may not caulk..usually
    not, or not continuously. in my experience caulk stops above eye level.
    check the top of a door frame & you'll see what I mean.

    there is a method of installing sheetrock known as ADA. air tight
    drywall approach. everything caulked, taped & floated for tight
    air barrier on interior of walls.

    sometimes we have to live with what we can't reasonably change...
    like lack of house wrap behind brick/vinyl. but what we can access
    is air sealing of walls from inside of house.

    there are times we get so focused on air sealing...that we lose
    sight of the bigger picture.
    simple things like the air barrier to the attic.
    you can't always seal all of it from the attic,
    so you come inside the living space & continue the seal from inside.
    clear caulk is a great thing! just wish there was a caulk that dried
    to a matte finish, instead of a shinny finish.

    even the fireplace, from the attic, seal what you can.
    then come inside and continue the seal.

    I often find leakage at ceiling moldings at top of brick fireplaces.
    After sealing opening at fireplace from inside the attic...I caulk inside the room
    @ fireplace.
    Mortor joints first, then once that dries, a continuous bead of caulk
    from molding to brick. then the top of the molding to the ceiling.
    between the attic sealing & the interior sealing... you can do a heck
    of an air sealing job. and a secondary line of defense is a good thing.

    during blower door test...these are areas to check for leakage.
    get on a ladder & feel at top of molding @ ceiling,
    @ bottom of molding @ wall. wet your hand so that you'll
    feel if air movement is slight.
    same with floor moldings. feel at floor of uncarpeted room & at top
    of molding to wall.
    feel the tops of door frames & window frames...you'll see what I
    mean about painter stopping caulk ...at eye level.

    now OP if you don't have ceiling moldings...this post has been a waste
    of time!

    I agree that ducts should be sealed. been thinking about that too.
    I wonder about ducts being depressurized @ 25 pa. and once ducts
    are pressurized...if the pressure was increased.
    it is hard to find leakage @ 25 pa. but up that pressure, and leaks
    are easier to find.
    108 cfm of duct leakage..spot on 5% for a 5 ton unit.
    and that doesn't come easy, sealing to 5% EVERYTHING has to be sealed.
    I've never tested a duct system that achieved 5% total duct leakage.


    as for the duct system, it is a sheet metal trunkline with flex supply ducts.
    I don't agree with removing all the insulation on ducts & trunkline
    in the attic, I do think that
    the ducts should be mastic sealed.

    unwrapping the sheet metal trunkline, mastic sealing every seam, re-insulating the
    trunkline..that is a lot of time effort & money.
    I think it could be better spent by mastic sealing flex duct collars, plenum corners,
    plenum seams & plenum connections to equipment.
    supply box penetrations & return air sealing.
    that is where I'd focus.

    these small leaks add up to a large leakage amount.
    you'll have to weigh costs vs benefits on some of this stuff.
    hopefully auditor/rater can weigh in on some of this based on their
    experience in your area.

    I'm not saying that these are the only solutions...just adding some
    food for thought. the whole no house wrap or anything on OSB walls..
    kinda threw me for a loop. once I moved past that...I started thinking
    about keeping air out of walls...blah blah blah.

    Have a wonderful Easter everyone...see y'all tomorrow evening.
    The cure of the part should not be attempted without the cure of the whole. ~Plato

  13. #78
    Join Date
    Oct 2006
    Location
    So. NH
    Posts
    748
    Erla - I agree, but up to this point the blower door and duct-blaster say this place is super tight, which is so contrary to all the symptoms. Puzzling.

    Just patiently waiting that next test now to see if there is an A-HA moment coming. If not this is going to go down as text book training exercise when it is figured out!

    The last "no house wrap house" unfortunately for me was mine! It had defective masonite siding and needless to say I replaced a lot of OSB. I can only imagine under that vinyl that isn't really waterproof there are, or going to be some holes going on. If it is part of the puzzle here I can't say for sure but obviously it's not good.

    Happy Easter to you as well.

Page 6 of 8 FirstFirst 12345678 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event