    Goodman HP sounds like airplane in defrost

    CPLE24-1C

    I've read long ago about units sounding like this , and think it was typically normal

    But I thought I'd make sure

    Its my dads house he just purchased , and he says it sounds like a jet landing when going into defrost

    Works fine otherwise

  2. #2
    Join Date
    May 2009
    Location
    Cummins, GA
    Posts
    1,552
    If the system isn't equipt with quiet shift....I would add the relays to allow the ODU to shut down during switchover to defrost.

    I checked your profile and found no email. Email or PM me and I will send you a step by step wiring diagram to install the proper relays for quiet shift.

  3. #3
    Join Date
    Apr 2004
    Location
    MN
    Posts
    1,829
    Brent, I would like to see those diagrams. Email in my profile. Thanks
    A Veteran is a person, who at some point in their life, wrote a blank check payable to the United States of America for payment up to and including their life.
    Gene Castagnetti-Director of the National Memorial Cemetery of the Pacific in Hawaii

  4. #4
    Join Date
    May 2009
    Location
    Cummins, GA
    Posts
    1,552
    Just sent it Doc.

  5. #5
    Join Date
    May 2005
    Location
    South Carolina
    Posts
    63
    Brent, I would also like to see those diagrams. Email in my profile. Thank You

  6. #6
    Join Date
    May 2009
    Location
    Cummins, GA
    Posts
    1,552
    Just sent Augie.

  7. #7
    Join Date
    Apr 2004
    Location
    MN
    Posts
    1,829
    Thanks Brent! And thanks to Rundawg!
    A Veteran is a person, who at some point in their life, wrote a blank check payable to the United States of America for payment up to and including their life.
    Gene Castagnetti-Director of the National Memorial Cemetery of the Pacific in Hawaii

  8. #8
    Join Date
    Jul 2009
    Location
    South Carolina
    Posts
    3,346
    Before changing the defrost to a soft start on that unit I would want to be 100% sure the RV is causing a problem during defrost & not the termination stat causing the head to go too high. That is an older 10 SEER & I'm pretty sure with a recip compressor & no factory hard start components. Of course the hard start can be easily added but I would manually shift the unit into defrost by shutting off the power to the condenser, jumping the RV into cooling mode & unplugging the fan & then putting the power back to it real fast just like it would happen on a soft defrost cycle. That would confirm whether the soft start defrost would solve your problem or not.
    Gary
    -----------
    http://www.oceanhvac.com
    An engineer designs what he would never work on.
    A technician works on what he would never design.