    Chilled water closed loop

    I am having a foaming discharge from my auto air purgers. Is this an indication of air infiltration?

  2. #2
    Join Date
    Jul 2003
    Location
    Orange County N.Y.
    Posts
    1,176
    Quote Originally Posted by crackerman View Post
    I am having a foaming discharge from my auto air purgers. Is this an indication of air infiltration?
    Either that or you popped a tube.

    ...Ron
    Roof Rat

  3. #3
    We recently did a eddy currrant test on condensor side it did not indicate any negative results.

  4. #4
    Join Date
    Aug 2009
    Location
    Prattville, Alabama
    Posts
    2,058
    Not to say you do or do not have a tube leak, but a leak at or near the end of the tube probably won't show on an eddy current test. And a leak between the tube and the endsheet won't either. That foaming discharge from the air purgers could be caused by a number of things. Since we don't know what refrigerant your chiller has, or the application (comfort? process?), or if the system has been disturbed (opened for repairs?), or what your operating pressures are (possible pump shaft seal leak), it is difficult to think of all the possibilities.

  5. #5
    Join Date
    Jan 2005
    Location
    Houston TX
    Posts
    874
    Did you try and put a leak detector in the not so close proximity of the foaming air bleeder. What are your system pressures (water side) is any part of it below atmospheric pressure ?
    Once in a while everything falls into place and I am able to move forward, most of the time it just falls all over the place and I can't go anywhere-GEO

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event