    Digi Cool AK 900 Manifold Rebuild

    My high side ball valve slowly leaks into my center port when closed on my AK manifold. Brenda mailed me replacement teflon seals and O-rings. I pulled the red dial off and unscrewed the brass pieces, but how do I access/replace the teflon ring? I couldn't find any posts on this.

  2. #2
    Join Date
    May 2009
    Location
    Savannah, Ga/H.H. Island, S.C.
    Posts
    1,488
    Shoot an email to Doug Lockhart via this or the Digi-cool website.

    Doug will point you in the right direction.

  3. #3
    Join Date
    Mar 2011
    Location
    Birmingham, AL
    Posts
    28
    Has anyone else replaced their teflon seal?

  4. #4
    Join Date
    Jan 2008
    Location
    In the work truck
    Posts
    3,010
    no did you try giving that nut a little turn to tighten it before you pulled everything apart? Thats all mine needed..
    Gotta have the right tool for the job!

    Where is all the stuff MADE IN THE USA?

    "Thats what we do Troy. Incredible, Invisible, Imbelivable things. We are an Unseen, Unknown, Unvincible fraternity of craftsman.."

  5. #5
    Join Date
    Mar 2011
    Location
    Birmingham, AL
    Posts
    28
    It was already tight. I unscrewed the nut and re-tightened. It still leaks. Didn't leak during the first 10 months.

  6. #6
    Join Date
    May 2010
    Location
    Canada
    Posts
    833
    Try some Nylog.

  7. #7
    Join Date
    Aug 2010
    Posts
    2,793
    Can you post pics of the leaking parts? After looking at other pictures, I have a gut feel that it uses the same manifold assembly OEM.

  8. #8
    Join Date
    Feb 2006
    Location
    USA
    Posts
    4,381
    Here's where mine was leaking from .. I've never exerted to much force either . .

    Haven't fixed it yet I need to though as the manifolds I have laying around do not line up and I hate the look with the angled fittings. Besides this I've had the issue of refrigerant bypassing the low side ball valve. Anyone know the point of the brass washer looking thing inside the area where the nut in the picture is?

    Sent from my SGH-T999L using Tapatalk 4

  9. #9
    Join Date
    Feb 2004
    Location
    Western New York
    Posts
    1,049
    Quote Originally Posted by hvac wiz 79 View Post
    Besides this I've had the issue of refrigerant bypassing the low side ball valve. ?
    I found with the supplied manifold, after you have metered in some liquid refrigerant and you show a little frost on the body, the suction side valve will not shut off 100%. Found this out the hard way- shut off the gas feed to a system, walked away for a few minutes to check the evaporator, and the refrigerant was still feeding into the system. OVERCHARGE!

    E-mailed Digi-cool and got no response.
    Last edited by baub; 09-10-2013 at 04:15 PM. Reason: spelling
    Experience is what you have an hour after you need it.

  10. #10
    Join Date
    Jun 2011
    Location
    Central Indiana
    Posts
    615
    I had to do this repair. My inner teflon seal failed and was blocking the lowside valve so no refrigerant would pass by the valve.

    Take out the hex keyed bolt from the side of the manifold. You will see a little brass plug. Let that drop out the end and then you will see the outer seal.

    Take a pick, like a dental pick or those cheap ones you can get at harbor freight and pull it out. A 120 degree hook pick works best. It will damage the seal so dont do this for fun, just when you need to replace them.

    Then pull off the knob from the front and under it is a 6 point bolt that can be removed. Wrench that puppy out of there and pull the whole assembly out.

    The ball part of the valve is under that assembly. Use the pick to guide the ball and drop it out the side, where the hex key bolt was.

    Then use the pick again to get the inner seal out. Its the same as the outer seal.

    To reassemble it, take one of the seals and put some nylog on the back of it and drop it in from the side of the manifold. Use the pick to get it to seat right. Be gentle, if you score the seal your screwed. If you cant figure out which side of the seal goes towards the ball, you shouldn't be in this business. If you made it this far and cant figure it out, sell the manifold and apply at McDonalds.

    Now comes the hard part. Drop the ball in the end of the manifold. It has a little stalk on it. Drop the stalk in first. Then use the pick to spin the ball from the front until the stalk points up to where the knob is supposed to be. It can be difficult and it can take a few trys to get it to slide in there right.

    Then install the outer seal. Again, use nylog. Put it on the side facing the ball. When you drop it in there, you will have to push it to get it to seat on the ball. I used a q-tip because I didnt want to mess up the seal but any thing small and not metal should work.

    Put the brass plug back in the end and then reinstall the hex keyed bolt. There is an o-ring on the hex keyed bolt, the rebuild kit comes with a new one. Nylog here too.

    Then take the 6 point bolt assembly and replace the o-ring on it and put it back on the front. You will have to line up the slot on the assembly with the stalk on the ball. Again, Nylog.

    Put the knob back on and then go out and make some money.
    The only true knowledge is the pursuit of knowledge

  11. #11
    Join Date
    Aug 2010
    Posts
    2,793
    Quote Originally Posted by hvac wiz 79 View Post
    Here's where mine was leaking from .. I've never exerted to much force either . .

    Haven't fixed it yet I need to though as the manifolds I have laying around do not line up and I hate the look with the angled fittings. Besides this I've had the issue of refrigerant bypassing the low side ball valve. Anyone know the point of the brass washer looking thing inside the area where the nut in the picture is?

    Sent from my SGH-T999L using Tapatalk 4
    Is that the piston rod? I would like to see the piston rod and a closeup of the bore?

  12. #12
    Join Date
    Mar 2007
    Location
    wedged in freezer shelf
    Posts
    6,743
    Piston? It's a ball valve.

  13. #13
    Quote Originally Posted by itsiceman View Post
    Piston? It's a ball valve.
    i was wondering the same thing, my Vanilla Gorilla

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event