    location of liquid drier

    as for 1 hp ductless air-con outdoor unit, after a compressor replacement after burnout, where shall I put the liquid line drier, somewhere in between condenser and capillary tube or after capillary tube ?

  2. #2
    Join Date
    Jan 2007
    Location
    N.E. KS
    Posts
    717
    Liquid line filters go before the metering device.
    Some people know the cost of everything but the value of nothing.

  3. #3
    Join Date
    Jan 2007
    Posts
    1,359
    Some ductless systems are not supposed to have a filter drier.. You should check with the manufacturer about it for your specific unit. We have already installed filter driers for 1 day after a compressor change out and then removed them.

  4. #4
    Join Date
    Jan 2007
    Location
    Kuala Lumpur, Malaysia
    Posts
    23
    actually which one is more suitable for the cleaning work after compressor burnout? liquid line or suction line drier ? or even both ?

  5. #5
    Join Date
    Jan 2007
    Posts
    1,359
    Quote Originally Posted by dknytech View Post
    actually which one is more suitable for the cleaning work after compressor burnout? liquid line or suction line drier ? or even both ?

    we do both liquid and suction along with a R-11 flush....
    then remove both filters after a day.

  6. #6
    Join Date
    Dec 2002
    Location
    Houston,Tx.
    Posts
    15,826
    And a good long vacuum probably would probably not hurt much either.
    __________________________________________________ _______________________
    “Experience is a hard teacher because she gives the test first, the lesson afterwards". - Vernon Law

    "Never let success go to your head, and never let failure go to your heart". - Unknown

  7. #7
    Join Date
    Jan 2007
    Posts
    1,359
    Quote Originally Posted by mrbillpro View Post
    And a good long vacuum probably would probably not hurt much either.
    yes i totally agree.. anything over 400microns is unacceptable.