    Ok i have a customer that i installed one of the new trane, amer. standard with 19 kw heaters with. The unit has worked like a dream through summer and winter until now. They live far away from me and i am trying to find out if i am correct on my over the phone diagnostic. I have a honeywell visionpro heat pump stat. All is sized correctly and wired correctly. Long story short. The heat pump runs fine, but all my strip heaters in the ahu, seemed to lock out the other day. this includes the emergency heat. I had customer reset line voltage to the unit, and all was well for 5 days. It did it again today. I had customer change the filter!!!!!!!!!!!!!!!!. "totally caked" he said over the phone. Does this ahu have a hard lockout if the strip heaters cycle off of the limit possibly more than once during a cycle. Hence the dirty filter. I have the manual at the job, or i wouldnt be begging for a reply. Thanks in advance.

  2. #2
    Join Date
    Jul 2009
    Location
    Columbia, MD
    Posts
    5,268
    Post Likes
    which model TAM unit? Do you have access to comfortsite? It's possible the limits are open.

  3. #3
    Join Date
    Jul 2007
    Location
    Virginia
    Posts
    9,021
    Post Likes
    Quote Originally Posted by heresjohnnyb View Post
    Ok i have a customer that i installed one of the new trane, amer. standard with 19 kw heaters with. Does this ahu have a hard lockout if the strip heaters cycle off of the limit possibly more than once during a cycle.
    I sent you an email to look at - check your inbox.
    Instead of learning the tricks of the trade, learn the trade.

  4. #4
    Join Date
    Aug 2012
    Location
    willowick ,oh
    Posts
    263
    Post Likes
    Thread Starter
    gravity i do have access to comfortsite, but its been a while and gotta remember the password lol.im trying to round up my actual #'s for the equipment. Rundawg, thanks for the info. Do you think that by cycling the power off and back on would reset the zeller relay. i seem to think it is a good possibility that it would.

  5. #5
    Join Date
    Aug 2012
    Location
    willowick ,oh
    Posts
    263
    Post Likes
    Thread Starter
    well it looks like the non cyclic, answered my question about resetiing from cycling power. Im thinking that this isnt what is causing the heaters to lock out. ok found it. model# aam7a0c42h31saa and the 20k heater kit. Can yall find me the ahu service and install pdf for the ahu. i want to review the diagnostics bayevbc20bk1aaa

  6. #6
    Join Date
    Jul 2007
    Location
    Virginia
    Posts
    9,021
    Post Likes
    Quote Originally Posted by heresjohnnyb View Post
    ok found it. model# aam7a0c42h31saa and the 20k heater kit. Can yall find me the ahu service and install pdf for the ahu. i want to review the diagnostics bayevbc20bk1aaa

    Check Your email.
    Instead of learning the tricks of the trade, learn the trade.

  7. #7
    Join Date
    Aug 2009
    Location
    Beatrice, NE
    Posts
    5,899
    Post Likes
    Doesn't the visionpro have a lock out setting where you can lock out aux heat above a selected outdoor temp?

  8. #8
    Join Date
    Aug 2012
    Location
    willowick ,oh
    Posts
    263
    Post Likes
    Thread Starter
    Yes it does but that is for aux and not emergency

  9. #9
    Join Date
    Aug 2012
    Location
    willowick ,oh
    Posts
    263
    Post Likes
    Thread Starter
    all heaters went out at this time, including emergency until power was cycled

  10. #10
    Join Date
    Aug 2012
    Location
    willowick ,oh
    Posts
    263
    Post Likes
    Thread Starter
    Thanks rundawg. you da man.