Results 1 to 10 of 10
-
03-14-2013, 07:43 PM #1
Professional Member*
- Join Date
- Aug 2012
- Location
- willowick ,oh
- Posts
- 163
amer. standard air handler heat locking out.
Ok i have a customer that i installed one of the new trane, amer. standard with 19 kw heaters with. The unit has worked like a dream through summer and winter until now. They live far away from me and i am trying to find out if i am correct on my over the phone diagnostic. I have a honeywell visionpro heat pump stat. All is sized correctly and wired correctly. Long story short. The heat pump runs fine, but all my strip heaters in the ahu, seemed to lock out the other day. this includes the emergency heat. I had customer reset line voltage to the unit, and all was well for 5 days. It did it again today. I had customer change the filter!!!!!!!!!!!!!!!!. "totally caked" he said over the phone. Does this ahu have a hard lockout if the strip heaters cycle off of the limit possibly more than once during a cycle. Hence the dirty filter. I have the manual at the job, or i wouldnt be begging for a reply. Thanks in advance.
-
03-14-2013, 08:42 PM #2
which model TAM unit? Do you have access to comfortsite? It's possible the limits are open.
-
03-14-2013, 10:17 PM #3
-
03-15-2013, 07:06 AM #4
Professional Member*
- Join Date
- Aug 2012
- Location
- willowick ,oh
- Posts
- 163
gravity i do have access to comfortsite, but its been a while and gotta remember the password lol.im trying to round up my actual #'s for the equipment. Rundawg, thanks for the info. Do you think that by cycling the power off and back on would reset the zeller relay. i seem to think it is a good possibility that it would.
-
03-15-2013, 07:33 AM #5
Professional Member*
- Join Date
- Aug 2012
- Location
- willowick ,oh
- Posts
- 163
well it looks like the non cyclic, answered my question about resetiing from cycling power. Im thinking that this isnt what is causing the heaters to lock out. ok found it. model# aam7a0c42h31saa and the 20k heater kit. Can yall find me the ahu service and install pdf for the ahu. i want to review the diagnostics
bayevbc20bk1aaa
-
03-15-2013, 08:11 AM #6
-
03-15-2013, 08:30 AM #7
Doesn't the visionpro have a lock out setting where you can lock out aux heat above a selected outdoor temp?
-
03-15-2013, 08:46 AM #8
Professional Member*
- Join Date
- Aug 2012
- Location
- willowick ,oh
- Posts
- 163
Yes it does but that is for aux and not emergency
-
03-15-2013, 03:12 PM #9
Professional Member*
- Join Date
- Aug 2012
- Location
- willowick ,oh
- Posts
- 163
all heaters went out at this time, including emergency until power was cycled
-
03-15-2013, 03:23 PM #10
Professional Member*
- Join Date
- Aug 2012
- Location
- willowick ,oh
- Posts
- 163
Thanks rundawg. you da man.