    copper repair

    I am wondering if there is a rule of thumb about how large a hole in a copper pipe you can braze over is. Sometimes a piece of pipe can be in a place that is tough to get cutters around or unsweating a joint then brazing back in is preferably avoidable like on a reversing valve. Is there some kind of guideline to let you know when the extra work is necessary? Like a 1/8 inch hole in a 3/4 pipe? Do the materials involved make a difference (soft/hard copper, 15/40% silver)?

  2. #2
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    4,509
    Your only guideline is experience with the torch
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Liberalism-Ideas so good they mandate them

  3. #3
    Join Date
    Oct 2010
    Location
    Anderson, South Carolina, United States
    Posts
    6,345
    Quote Originally Posted by 2sac View Post
    Your only guideline is experience with the torch
    X2, the siding guys drove a roofing nail through my suction line inside the wall right at the top plate the other day, I had to take down the siding, cut the osb, and there was no way to cut it so I dropped some 15% on it and all is well.

  4. #4
    Join Date
    Feb 2013
    Location
    Lamar, SC
    Posts
    491
    That's the answer I was hoping for.

  5. #5
    Join Date
    Jul 2012
    Location
    Western KY
    Posts
    1,221
    A hole is ok to patch up. How big? As big as you can get solder to cover without falling in. A crack should alway be cut out IMHO.

  6. #6
    Join Date
    Sep 2005
    Location
    Atlanta GA area
    Posts
    20,857
    Quote Originally Posted by 2sac View Post
    Your only guideline is experience with the torch
    Quote Originally Posted by jtrammel View Post
    X2, the siding guys drove a roofing nail through my suction line inside the wall right at the top plate the other day, I had to take down the siding, cut the osb, and there was no way to cut it so I dropped some 15% on it and all is well.
    Quote Originally Posted by Tommy knocker View Post
    A hole is ok to patch up. How big? As big as you can get solder to cover without falling in. A crack should alway be cut out IMHO.
    Above covers the subject from my view. Sometimes we just have to do what we can. I have removed a short section, brazed up a hole, and brazed a scrap of CO onto a larger hole.

    One cool trick (takes a little practice) I did on a 7/8 suction line: I took a 7/8 coupler, took my tin snips and cut out about 1/3 of the circumference. Then cut it down to around square (if it was flat). Then bent it back to the proper curve. Brazed this onto a hole too large to fill with brazing material. Worked fine.

    Key issue is CLEANLINESS! Brazing always works better when the surfaces are clean.

    And remember the higher the silver content of the rod, the better gap filling as well as better adhesion.

    Practice is a good thing.... might play with it a bit when you have time.
    GA-HVAC-Tech

    Quality work at a fair price with excellent customer service!

    Romans Ch's 5-6-7-8

    2 Chronicles 7:14

  7. #7
    Join Date
    Nov 2004
    Location
    Skokie , IL near chicago
    Posts
    1,126
    Quote Originally Posted by ga-hvac-tech View Post
    Above covers the subject from my view. Sometimes we just have to do what we can. I have removed a short section, brazed up a hole, and brazed a scrap of CO onto a larger hole.

    One cool trick (takes a little practice) I did on a 7/8 suction line: I took a 7/8 coupler, took my tin snips and cut out about 1/3 of the circumference. Then cut it down to around square (if it was flat). Then bent it back to the proper curve. Brazed this onto a hole too large to fill with brazing material. Worked fine.

    Key issue is CLEANLINESS! Brazing always works better when the surfaces are clean.

    And remember the higher the silver content of the rod, the better gap filling as well as better adhesion.

    Practice is a good thing.... might play with it a bit when you have time.
    oh yea , i did this trick on a 5/8 tube imbedded in concrete for radiant heat....worked great....use minimum of 15% silfos , used correctly it flows like butter.....Jack
    B[COLOR=a friend is one who knows us , but loves us anyway

  8. #8
    Join Date
    Feb 2013
    Location
    Lamar, SC
    Posts
    491
    I like the copper patch idea for larger holes. Thanks for all your input everyone.

  9. #9
    Join Date
    Sep 2005
    Location
    Atlanta GA area
    Posts
    20,857
    Quote Originally Posted by ga-hvac-tech View Post
    Above covers the subject from my view. Sometimes we just have to do what we can. I have removed a short section, brazed up a hole, and brazed a scrap of CO onto a larger hole.

    One cool trick (takes a little practice) I did on a 7/8 suction line: I took a 7/8 coupler, took my tin snips and cut out about 1/3 of the circumference. Then cut it down to around square (if it was flat). Then bent it back to the proper curve. Brazed this onto a hole too large to fill with brazing material. Worked fine.

    Key issue is CLEANLINESS! Brazing always works better when the surfaces are clean.

    And remember the higher the silver content of the rod, the better gap filling as well as better adhesion.

    Practice is a good thing.... might play with it a bit when you have time.
    Quote Originally Posted by rojacman View Post
    oh yea , i did this trick on a 5/8 tube imbedded in concrete for radiant heat....worked great....use minimum of 15% silfos , used correctly it flows like butter.....Jack
    Quote Originally Posted by jmsmars1 View Post
    I like the copper patch idea for larger holes. Thanks for all your input everyone.
    Rojacman's post reminded me of something I did last year. Off season, I agreed to replace a DWH (water heater) for 'grandma' of one of my customers. Took it out and was drilling a hole through the wall for the draimpan drain... cut the supply hot water line (all plbg in the slab). What to do? Chipped the slab back a bit, cut apart a 3/4 CO water pipe fitting, and brazed it onto the leak. Worked fine.

    The interesting thing of this: When I opened up the wall to do the plumbing repair, we found the wall was very wet inside. Seems the flue vent above the DWH was not flashed correctly and leaking. Long story short... ended up doing a $5000 repair on the house. Not exactly HVAC work... however in off season it was nice income.

    I used to run a remodeling co, so this was just a matter of pulling out some tools in storage and going to work. My HVAC install crew appreciated something to do (earn some $$$), and the customer was very happy to get it fixed.
    GA-HVAC-Tech

    Quality work at a fair price with excellent customer service!

    Romans Ch's 5-6-7-8

    2 Chronicles 7:14

  10. #10
    Join Date
    Jul 2010
    Location
    So-Cal
    Posts
    576
    Havent tried it but a friend told me if its a large hole he would strip a piece of copper wire and wrap that around the pipe where the hole is and braze over that.
    Sounds like it would work!

  11. #11
    Join Date
    Jul 2012
    Location
    Western KY
    Posts
    1,221
    Quote Originally Posted by jackintheboxtec View Post
    Havent tried it but a friend told me if its a large hole he would strip a piece of copper wire and wrap that around the pipe where the hole is and braze over that.
    Sounds like it would work!
    I like that!! Good idea.

  12. #12
    Join Date
    Oct 2011
    Location
    Las Vegas, NV
    Posts
    467
    Quote Originally Posted by jackintheboxtec View Post
    Havent tried it but a friend told me if its a large hole he would strip a piece of copper wire and wrap that around the pipe where the hole is and braze over that.
    Sounds like it would work!
    Interesting. I like that. I've used the patch trick before, but never that one.

    Sent from my PG86100 using Tapatalk 2

  13. #13
    Join Date
    Sep 2005
    Location
    Atlanta GA area
    Posts
    20,857
    Good idea! Winding some, say, 12 or 14 GA single strand CO wire around a hole... then braze the bundle... That would be less work than cutting and forming a patch. And probably easier to braze also.

    I always have some Romex on the van, for repairing electrical stuff around a furnace. Just strip it, wind it, and braze (well sand clean the CO pipe also). Probably could do this with a Dyna-flow rod rather than 15% or 45%... thus saving rod cost.

    THX for posting it.
    GA-HVAC-Tech

    Quality work at a fair price with excellent customer service!

    Romans Ch's 5-6-7-8

    2 Chronicles 7:14

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event